Quote
i cant remember how many AC units I have seen in the world that have #10 running off a 40 or 50A breaker..
Depending on the A/C unit nameplate data, this may be compliant.
90.8(A) does not contain the mandatory term SHALL but it is always good practice to plan wiring systems for the future.


John