Those breakers don't require a neutral on the load side to work correctly. They look at the current on the two hots and the neutral to see if these currents sum to ~0. Even if one of the 3 load conductors does not have current or is not connected, the current on the other two will still sum to ~0. When the current sum gets to 30mA, the breaker will open the circuit.