given a GFPE, what if the circuit is 240 vac single phase (heat trace) WITH NO neutral?
if there is no neutral in the circuit these require a special breaker with NO neutral...
a GFPE breaker with a neutral requires a neutral in the circuit to work properly the way i understand it..
the breaker i have is a two pole cutler hammer with a neutral...the problem with the circuit i am working with is that there is no neutral so this type of breaker is not the correct type in my opinion...we have a lot of heat trace using these breakers but there is no neutrals in any of the circuits...
in my opinion this breaker will only work on overcurrent..with no neutral..