Hello Jerry,

Based on 1999 NEC I’m going to give my opinion and if anyone sees I’m wrong please step in.

Section 440-4(b) says the manufacturer shall provide a nameplate with the minimum supply circuit conductor ampacity, along with other info. 110-3(b) requires equipment to be installed to this minimum.

Since you say the nameplate info given is, “Minimum Circuit Ampacity: 22 amps” I would use #12 AWG CU and I believe this would be code compliant with (310-16).