The title of the section on the other site is "switch replacement". The code requirement to reidentify the white wire in this application first appeared in the '99 code. If the installation was made under prior codes there was no requirement to reisdentify the white. I can't tell for sure if there is a ground wire in the box or not. There is no requirement that the EGC be connected directly to the switch, it is only required to be connected to the metal box. It also could be old enough that 2 wire no ground NM cable was used. The wording on the site makes it clear to reconnect the ground wire if there is one. If there is not an EGC, some additional wording should be added for compliance with the exception to 404.9(B). This would require the use of a nonmetallic face plate when replacing a switch at an outlet without an EGC.