Take a look at Appendix D, example 1 "Minimum # of branch circuits required" covers things quite well. Note that the minimum number of general purpose circuits for lighting loads (this includes most receptacles) works out to one 15 amp circuit for every 600 square feet or one 20 amp circuit for every 800 square feet.