Glenn, it would be fine if Doug could get the POCO to do this, but this is not a difficult task

We do this all the time it is just the norm here.

Personally if it is not specked otherwise I would use Schd 80 PVC up the pole and at the meter with metallic 90's underground at both locations.

I would rig a pulley above the pole riser with a choker so all pulling and feeding can be from the ground.

Roger