Posted By: DougW Question about mixing RNC & RMC... - 04/04/05 07:09 PM
specifically as physical protection for a service lateral.

Still working on the new service for the parsonage garage - getting yanked between the PoCo and AHJ. Business as usual I suppose!

The latest development: I had contacted ComEd and they had said that they could trench & place the run from the pole to the garage, but at a significant expense... mostly the trenching time. I JULIE's the site, and got the AHJ OK to trench. I called ComEd back to see if they could just drop the URD in the trench.

They responded that they had reviewed the site, and, since the majority of the property was commercial, I, as the contractor, would be responsible for placing the lateral, and that the AHJ would have the say-so on the conductors.

I priced out URD, and got a fair price from my local house.

Back to the AHJ - they said that the only folks who could bury a lateral (even 24"+) was ComEd, due to liability concerns. If the homeowner or contractor did it, it needed to be in conduit, either RMC/IMC (required for grade penetration & above) buried 18", or RNC at 24", with Cu conductors throughout. (bye bye affordable Al)

With 1 1/2" RMC @ $520/100', and 1 1/2" RNC @ $52/100', my thought was to combine the two - use metal for the risers and elbows at either end, and PVC for the horizontal run - the long and expensive part. I'm renting a trencher, so depth = extra labor isn't an issue.

My question is this - is an additional bonding means between the RMC elbow and riser at the pole and the RMC elbow and riser at the structure required? Should I sink grounding electrodes at each end to be safe? I can't find anything in the AHJ's electrical ordinance or the ComEd installation handbook, and I want to make sure I'm doing this run the right way. I've got calls in to ComEd and the AHJ, but I figured I'd troll for info here while I'm waiting.

Thanks for the help,

Doug
Posted By: gfretwell Re: Question about mixing RNC & RMC... - 04/04/05 08:01 PM
If you maintain the metal raceway all the way to the cabinet at the load end and use bonding bushings it would seem you are bonded. You should be able to bond to the POCOs ground at the pole.
Posted By: earlydean Re: Question about mixing RNC & RMC... - 04/04/05 08:14 PM
Bonding to a ground rod is called grounding and does no good. 250.86 of the NECode requires isolated 90s above 18 inches of cover to be bonded to the grounding or grounded conductor to minimize shock hazards in the event of a fault. This can be accomplished most easily by extending the RMC from the 90 up to the metal enclosure at the building, and up the pole at the utility end. Grounding bushings and jumpers sized from 250.66 at both ends will complete the job.

It is far less expensive to install PVC 90s.
Posted By: Active 1 Re: Question about mixing RNC & RMC... - 04/04/05 11:07 PM
Hey Doug,

I know some EC do the underground but I could never make it work dollar wise.

Like you said when the utility does the underground they just burry the AL sometimes undersized and they are done. For the EC to do it all different rules apply. It needs to be copper and in pipe. Conductores sized per NEC and inspected.

Last one I priced was something like this:
$2,200 ComEd does all underground work
$1,900 If we trench it 60' around trees
$1,600 If we trench, pipe, and back fill; they pull their AL wires
$1,000 If we trench, pipe, pull CU, back fill; they will run the wires up the pole and do final connections

Maby the numbers are off a bit but the point is if I bought the material, permits, rented trencher there was not enough left for the labor and proffit.

A subcontractor for ComEd told us when they do work for the utility they only have to meet the utility standards. When they do customer work they have to do what we spoke about above.

Yes, sometimes the utility yanks you around. When a job is proposed like this I believe it is assigned to a utility salesperson. They look at the job and try to get as much as they can. They don't seem to give you all your options or an honest answer.

The good news is when the utility does the work it is billed right to the customer on his electric bill. I just tell the customer what they charge is between you and the utillity.

Don't forget to figure going underground with the phone or cable if desired.

I know you can get 2" RMC for $50-55 or AL 2" RMC for $30. I want to say 1 1/2 should be in the $30 range.

What size service / conductors are you doing 100 amp?

If you need to use a ridgid or PVC bender or threader let me know.

Tom
Posted By: Roger Re: Question about mixing RNC & RMC... - 04/04/05 11:45 PM
Doug, as stated, you can stay with metal after the 90's if you want too and use bond bushings or what ever it takes to assure a grounded conduit to the enclosures, or you can change back to PVC.

You won't need to bond the metallic 90's if the shallowest part of the 90 is below 18" from the surface, see 250.86 Exception No.3

I would definitely stay with a metal 90 at the end you are going to pull from to prevent burn through.

Roger
Posted By: Dave55 Re: Question about mixing RNC & RMC... - 04/05/05 12:52 AM
I haven't checked lately, but my past experience is that ComEd can do it for less than I would want to. Especially nice is the fact that they will also be responsible for the installation. You wouldn't want to do this one over on warranty.

If you decide to do it, you might be able to glue the PVC together at grade, pull the wires through, then glue the PVC elbows on & slide it in the trench. That way there is no burn through & no bonding issue.

Dave
Posted By: Roger Re: Question about mixing RNC & RMC... - 04/05/05 01:46 AM
Dave,
Quote
If you decide to do it, you might be able to glue the PVC together at grade, pull the wires through, then glue the PVC elbows on & slide it in the trench. That way there is no burn through & no bonding issue
unfortunately that is a violation of 300.18(A).

Roger
Posted By: gfretwell Re: Question about mixing RNC & RMC... - 04/05/05 02:15 AM
Roger, that is why it is better to let the POCO do it. They don't care about the NEC.
We see 4/0 THHN in 2" here all the time, from the FPL sub. They do exactly what Dave said. They pull in the long straight part. cut it to length, then glue on the elbows and knock it in the trench with the Mini Kabota. Set the risers and backfill.
Posted By: DougW Re: Question about mixing RNC & RMC... - 04/05/05 04:11 AM
Great responses, but I fear that I didn't illustrate my idea completely...

At Pole: 10' Above grade RMC
Additional RMC to get to 24" depth
Metal 90
Transition to PVC Sched 80 RNC
(40', 1 bend, (probably metal,
unbonded per 250.86 Exception No.3
and then another 18')
Transition to RMC 90
RMC riser to
Meter enclosure (or to bushed entrance that is bonded to service cabinet.

I know that attaching a chunk of the raceway to a ground rod is grounding - the question I had was if anybody thought it neccessary to run an additional bare 6 AWG Cu with the conductors that was attached to bonding bushings (or soldered per ComEd) at the metal riser at the pole and at the meter enclosure.

ComEd originally told me they'd do the work, and that's what I told my customer - apparantly someone's mind got changed. Good thing I told them to expect an additional charge for the service drop/lateral installation. My bid's just for tearout, the panel and interior conduit so far.

I was told because it's classed as "commercial", the contractor is responsible for running the lateral.

As folks here (and the AHJ) have said - the PoCos follow their own rules, because it's on them, liability-wise.

[This message has been edited by DougW (edited 04-05-2005).]
Posted By: Active 1 Re: Question about mixing RNC & RMC... - 04/05/05 02:16 PM
I would still think you would have the option of Com Ed doing the underground. They would charge you for this. Underground upgrades are not free. Maybe the problem is the customer wanted the lateral upgraded/replaced/repaired for free by the utility. The sales person tired of saying no gave an excuse of "we don't do comercial laterials".

Dave has a point about warranty. If the utility does the lateral they are responcable for maintaining it. It the EC does it then the customer is allways responcable for it.

If you want a utility sub to price it out try Trench-it in Lakemore, Il.

As far a RMC up the pole it's been done that way but is that what the utility wants you to do? They told me to end near the pole underground with no 90 and they will go up the pole with a wire guard. I see the wire guard most often.

As for on the merer side you did not say what the set up was. Make sure you don't pipe right into the bottom of the meter without a way for expansion. The old undergrounds were done this way. Some had an expansion pipe. Things move in the ground the wires become too short and things break. The whole idea of the underground meter raceway was to allow an "s" shape of slack for ground movement. So be sure to leave litle extra slack at the meter.

Tom
Posted By: Roger Re: Question about mixing RNC & RMC... - 04/05/05 04:26 PM
Glenn, it would be fine if Doug could get the POCO to do this, but this is not a difficult task

We do this all the time it is just the norm here.

Personally if it is not specked otherwise I would use Schd 80 PVC up the pole and at the meter with metallic 90's underground at both locations.

I would rig a pulley above the pole riser with a choker so all pulling and feeding can be from the ground.

Roger
Posted By: DougW Re: Question about mixing RNC & RMC... - 04/05/05 07:59 PM
AHJ says 10' AG of RMC or IMC up the pole. Luckily, in the Rulebook, I only have to extend conductors 3' beyond a customer installed riser for PoCo hookup - if it was URD, I'd have to allow an extra 35' at the base of the pole. [Linked Image]

Still waiting for an answer from the PoCo - all the ilustrations show loose cable entering a pedestal base (duh) - with the AHJ wanting RMC at each end, maybe I'll be running a riser into an overhead style meter cabinet.


Hey... I just try to think of it as a learning experience! [Linked Image]

[This message has been edited by DougW (edited 04-05-2005).]
Posted By: nesparky Re: Question about mixing RNC & RMC... - 04/05/05 11:27 PM
We do this all the time on commercial properties. Here the POCO goes to the property line. It is then the EC to got to the building.
What we usually use is PVC schedule 40 in the trench and schedule 80 above the 90. If the run is <150' we use PVC 90s. We run the PVC up at least 8' up the pole and pull enough wire to go to the X formers. At the meter end we use a PVC expansion joint and run either sched 40 or 80 to the meter socket depending on pottential for damage inthe area. Sometimes if the potential for damage is high at either end we use RGS in place of the PVC above ground level. (have had too many corroded pipes in the ground to want metal in the ground)
It's not that bad of work and makes for an good looking job. Just make sure you charge enough.
A little extra wire in the meter socket does not hurt either.
Good luck

[This message has been edited by nesparky (edited 04-05-2005).]
Posted By: russ m Re: Question about mixing RNC & RMC... - 04/06/05 12:21 AM
I require a ground wire pulled with the lateral, and then bonded to RMC on the pole.

How it's attached to the pole depends on how the poco wants the wire on the pole side.
If it's a service head then I allow a pipe clamp or exotheric weld. If it's covered with their plastic strip, a grounding bushing is ok.
Posted By: DougW Re: Question about mixing RNC & RMC... - 04/06/05 04:14 AM
Just re-reading some of the posts.

Tom - Thanks for the equipment loan offer!

Was originally planning on #2 Cu, but after reviewing the Code, it looks like I can pull #4 Cu and be OK for a 100A service... of course, that's for a "dwelling unit", but I'll see what the AHJ says.

It's a 2 car detached garage with a gravel floor and almost no spare room inside. The biggest thing the current pastor is anticipating is maybe a 110 air compressor, and the door openers.
Posted By: Active 1 Re: Question about mixing RNC & RMC... - 04/06/05 04:43 AM
How about #3 wire. Single phase you could run 1 1/4". I looked today 1 1/4 RNC was $24 and $30 for 1 1/2.

Tom
Posted By: Dave55 Re: Question about mixing RNC & RMC... - 04/06/05 05:22 PM
Right you are, Roger. Thanks for the code lesson.

Dave
Posted By: DougW Re: Question about mixing RNC & RMC... - 04/07/05 02:52 AM
I'll ask about #3, Tom. Thanks.

Thanks to everyone for the input. It's not a difficult gig, just the same tasks in a little different format than what I've done previously.

Thanks again!
Posted By: iwire Re: Question about mixing RNC & RMC... - 04/07/05 08:35 AM
Russ

Quote
I require a ground wire pulled with the lateral, and then bonded to RMC on the pole.

Why would you (and can you?) require a 'ground wire' to be pulled when there is a grounded conductor already in the raceway?

To be effective this 'groundwire' would have to be sized based on Table 250.66.

Using the grounded conductor to bond the riser raceway would be the most effective method.

Quote
250.142 Use of Grounded Circuit Conductor for Grounding Equipment.
(A) Supply-Side Equipment. A grounded circuit conductor shall be permitted to ground non–current-carrying metal parts of equipment, raceways, and other enclosures at any of the following locations:

(1)On the supply side or within the enclosure of the ac service-disconnecting means

Bob