FYI, I've had to perform a lot of Sidewall Bearing Pressure calcs. I won't allow yellow 77 on ANY MV cables. 77 just does not really cut it in comparison. There were several instances where we would have to install additional manholes because we greatly exceeded the SWBP of the cable manufacturers if not for the polywater.

Good Stuff