Thanks for your posts,
I knew I was right. I called the inspector personally and asked specifically if he wants me to install a double pole breaker.
I wanted to talk to him to get a feel if he knew what he was talking about. Sometimes the inspectors have to inspect the plumbing, framing and electrical and they usually don't know to much about electrical.
I was suprised by him because he was talking about sharing a neutral and explaining how there could be a potential load on the neutral if both circuits are not turned off. So he sounded like he knew what he was talking about.
I don't like to tick these guys off. I just calmly explained that I didn't think it was right because if there is an overload or a short in one circuit, then both circuits would turn off and cut power off to the whole addition.
He still persisted in the double pole breaker so that is what I did. I can always go back and put the two single pole breakers on after we get the green tag. But I don't want to waste my time and money.
Just some of the obstacles us contractors have to go thru to get a job done.
Tev
|
|
|
Entire Thread
|
Failed Inspection, need two pole breaker
|
straightedge
|
09/16/03 07:19 PM
|
Re: Failed Inspection, need two pole breaker
|
Ryan_J
|
09/16/03 07:57 PM
|
Re: Failed Inspection, need two pole breaker
|
Electricmanscott
|
09/16/03 09:30 PM
|
Re: Failed Inspection, need two pole breaker
|
Bill Addiss
|
09/16/03 10:26 PM
|
Re: Failed Inspection, need two pole breaker
|
straightedge
|
09/16/03 10:33 PM
|
Re: Failed Inspection, need two pole breaker
|
HotLine1
|
09/16/03 10:39 PM
|
Re: Failed Inspection, need two pole breaker
|
iwire
|
09/16/03 10:41 PM
|
Re: Failed Inspection, need two pole breaker
|
Bill Addiss
|
09/16/03 11:34 PM
|
Re: Failed Inspection, need two pole breaker
|
LK
|
09/17/03 02:29 AM
|
Re: Failed Inspection, need two pole breaker
|
ThinkGood
|
09/17/03 02:32 AM
|
Re: Failed Inspection, need two pole breaker
|
iwire
|
09/17/03 02:52 AM
|
Re: Failed Inspection, need two pole breaker
|
Bill Addiss
|
09/17/03 03:15 AM
|
Re: Failed Inspection, need two pole breaker
|
Electricmanscott
|
09/17/03 10:06 AM
|
Re: Failed Inspection, need two pole breaker
|
ThinkGood
|
09/17/03 10:27 AM
|
Re: Failed Inspection, need two pole breaker
|
Ryan_J
|
09/17/03 01:43 PM
|
Re: Failed Inspection, need two pole breaker
|
resqcapt19
|
09/17/03 03:41 PM
|
Re: Failed Inspection, need two pole breaker
|
Bjarney
|
09/17/03 05:14 PM
|
Re: Failed Inspection, need two pole breaker
|
iwire
|
09/17/03 06:42 PM
|
Re: Failed Inspection, need two pole breaker
|
HotLine1
|
09/17/03 06:46 PM
|
Re: Failed Inspection, need two pole breaker
|
resqcapt19
|
09/18/03 01:39 AM
|
Re: Failed Inspection, need two pole breaker
|
spkjpr
|
09/18/03 01:51 AM
|
Re: Failed Inspection, need two pole breaker
|
iwire
|
09/18/03 05:59 PM
|
Re: Failed Inspection, need two pole breaker
|
triple
|
09/18/03 09:08 PM
|
Re: Failed Inspection, need two pole breaker
|
resqcapt19
|
09/19/03 02:02 AM
|
Re: Failed Inspection, need two pole breaker
|
iwire
|
09/19/03 09:50 AM
|
Re: Failed Inspection, need two pole breaker
|
resqcapt19
|
09/19/03 08:13 PM
|
Re: Failed Inspection, need two pole breaker
|
iwire
|
09/19/03 10:45 PM
|
Re: Failed Inspection, need two pole breaker
|
LK
|
09/19/03 10:58 PM
|
Re: Failed Inspection, need two pole breaker
|
resqcapt19
|
09/20/03 03:10 AM
|
Re: Failed Inspection, need two pole breaker
|
iwire
|
09/20/03 07:21 PM
|
Re: Failed Inspection, need two pole breaker
|
iwire
|
09/20/03 07:40 PM
|
Re: Failed Inspection, need two pole breaker
|
LK
|
09/20/03 10:45 PM
|
Re: Failed Inspection, need two pole breaker
|
Roger
|
09/20/03 11:27 PM
|
Re: Failed Inspection, need two pole breaker
|
iwire
|
09/21/03 01:23 PM
|
Re: Failed Inspection, need two pole breaker
|
LK
|
09/21/03 03:10 PM
|
Re: Failed Inspection, need two pole breaker
|
Pinemarten
|
09/23/03 11:58 AM
|
|
Posts: 46
Joined: March 2013
|
|
|
|