The short answer is yes
You say "feeder" (indicating you are on the load side of the service disconnect) so you will be using 225.32 but if this is really a service lateral (line side of the service disconnect) they are service conductors and you are in 230.70(A)(1)
It is really a distinction without a difference tho.
Both say the same thing

Quote
The disconnecting means shall be at a readily accessible location nearest the point of entrance of the conductors.


There is some debate about what "nearest the point of entrance" means but it isn't 20 feet. IMHO


Greg Fretwell