hmm.. would this be more appropriate?
heater 2500 / 240 = 10.4 AMPS. x 1.25 for continuous load = 13.
since 15AMP breaker is max 12AMP at 80% load.
Isn't #12 the more correct choice since it can handle up to 16 amp?