You have to look at the connected load. If a significant part of the connected load is line to line only you can safely downsize the neutral but since (2005?) they say in addition to the 220.61 calculation (to provide overload protection), 250.122 will be the minimum size (to provide short circuit protection).


Greg Fretwell