wewire2;

Thanks for the response!

Man, I don't know why I placed the 250.120(C) reference!
I do not remember smoking any Crack - never smoked it before AFAIK wink

Per the Section reference, the following Addendum is issued:

"#6 and smaller to be continuously Color Coded (Insulation Color to be Green)...
Section = 250.119."

Text verbatim:

"Individually covered or
insulated equipment grounding conductors shall have a
continuous outer finish that is either green or green with
one or more yellow stripes except as permitted in this
section.
{A}

Conductors with insulation or individual covering
that is green, green with one or more yellow stripes, or
otherwise identified as permitted by this section shall not
be used for ungrounded or grounded circuit conductors."


Exception to the above Mandatory Note {A} is 250.119(A); EGCs larger than #6.

Now I must consume Raven (eat Crow), so I must go!

Scott