Hi Yoop.
695.6(F). says ..fire pump controller and fire pump transfer switch,where provided,shall not serve any load other than the
fire pump for which it is intended.

same generator is fine.
Now the can of worms. That generator now becomes 'Emergency' power.Not standby.Now comes all the documentation of all testing and maintenance requirements.