Reno:

With the exception of one job, with one transformer, in my life as an EC, all transformer installs had OCP on primary and secondary. It was a matter of design and choice, mot NEC compliance.

The AIC of the secondaries is a calculation, I used and still do Bussmanns Point-to-point method.



John