Posted By: matt_b OCPD on secondary? - 11/17/09 07:24 AM
So I have been lurking the site for a while and I now have an issue at work I could use some input on.

The gear we submited was 3 sections: pull, meter, main and distribution.

Instead we got gear with an extra section for the main.

soooo... we know have to move a 300kva xfmr which is fed from 500A breaker 480 delta, to 1000A 280/120Y distribution panel. we have to move it to a utility room about 50ft away.

it had to get "re-enginered" but the engineer drew up a 1200AS/1000AF for the primary, and no OCPD on the secondary?

NEC 240.21 - 10ft tap rule
408.16
450.3(A)

all seem to tell me that if there is a 1000AF on the primary, i need a disco on the secondary within 10ft?

THOUGHTs?

matt
Posted By: KJay Re: OCPD on secondary? - 11/19/09 12:29 AM
Well... I think you should probably be using Table 450.3[B], since the voltage is 480 and not over 600V.
Also, if the transformer primary conductors are fed directly from OCP bolted to the main bus of the switchgear, I don’t believe that would be considered a tap, so 240.21 most likely wouldn’t apply here.

The engineer probably had other manufacturers data available when laying out the design, but I would still keep a change-order handy, just in case the inspector has an issue with the design. wink
Posted By: Scott35 Re: OCPD on secondary? - 11/19/09 10:38 AM
Matt;

Welcome to ECN!

First off, I would like to clarify a few things, per the EE's Design.

Does the Single Line show the 300 KVA Transformer having Over Current Protection for the Feeders only on the Primary Side Feeders, or Both Primary and Secondary Side Feeders?

Since the Separately Derived System ("SDS") is "Dual Voltage", the Primary Over Current Protection cannot be used to protect the Secondary side feeder Conductors.

Since the Secondary rating is 208Y/120V, there will need to be Over Current Protection for the Feeder Conductors on the Secondary side - as well as the Primary side.

Example setup + values for OCPD (Over Current Protection Device):

300KVA Transformer;
Primary rating = 360 Amps @ 480V 3 Phase 3 Wire.
Secondary rating: 830 Amps @ 208V (208Y/120V 3 Phase 4 Wire).

Maximum Primary side OCPD: 900 Amps (250% of 360 Amps) - refer to Table 450.3(B).
Primary Feeder Size: 500 MCM THHN Cu. or equivalent parallel conductors.

Maximum Secondary side OCPD: 1200 Amps (125% of 830 Amps, brought up to the next highest common OCPD rating).
Secondary Feeder Size: (3) sets of 500 MCM THHN Cu, or equal.

Basically, if the Single Line shows OCPD on the Primary Side only, the Design is not compliant, since the Secondary is Dual Voltage (208/120V).

If the Secondary was a Single Voltage - such as 240V 3 Phase 3 Wire, then the Primary OCPD could protect the Secondary Feeder Conductors, and the design would be compliant.

Since it appears that the Secondary is Dual Voltage, the Secondary Feeder Conductors require OCPD.

This may be done in Two different ways:
  1. 1200 Amp Feeders brought directly from Transformer, to a 1200 Amp OCPD (Circuit Breaker or Fusible Safety Switch).
    This option would relate to feeding a gear section from the Transformer, and the gear contains a 1200 Amp "Main Breaker" or "Main Fusible Switch".
    *** FYI, The OCPD does not have to be an intregral part of the gear - it may be separate equipment. The OCPD must be "In Front Of" (on Line Side of) the gear section.
  2. Separate feeders - say of 400 Amp capacity, brought out of Transformer, and run to individual Panelboards - each Panelboard contains a 400 Amp Main Breaker (or Fusible Safety Switch with 400 Amp Fuses).


Review the Single Line for this information, and let us know what's indicated.

As it stands, this issue requires an RFI submitted to the EE, requesting clarification for Primary & Secondary Conductors' OCPD.
Reference NEC Article 450 & Table 450.3(B) in the RFI document.

Good luck.

Scott
Posted By: KJay Re: OCPD on secondary? - 11/20/09 04:37 PM
I was under the impression that this was an industrial high bay type installation, but that was an assumption on my part so, maybe not.
Posted By: HotLine1 Re: OCPD on secondary? - 11/21/09 04:48 AM
Scott:
Could you please explain the methodology for a MOCP of 1200 amp, on three (3) sets of 500KCmil, with 75 degree terminations. 500 KCmil Cu is 380 amps, which is compliant for 400 amp OCP. 2 sets would be compliant for 800 amp OCP, but 3 sets only total 1140 amps, and being >800 amps, a lower OCP is required, right?

Posted By: frenchelectrican Re: OCPD on secondary? - 11/21/09 07:52 AM
Originally Posted by HotLine1
Scott:
Could you please explain the methodology for a MOCP of 1200 amp, on three (3) sets of 500KCmil, with 75 degree terminations. 500 KCmil Cu is 380 amps, which is compliant for 400 amp OCP. 2 sets would be compliant for 800 amp OCP, but 3 sets only total 1140 amps, and being >800 amps, a lower OCP is required, right?



If I did recall the NEC code reguarding of any conductors using over 800 amp the conductor have to be sized to match or excessed of the OCPD and with 3 X 500KCM ( 240mm²) I don't think it will meet the code with 75°C rating and the only way it can meet the code you have to upsize the conductors like 3 X 600KCM ( 300mm²) then it will meet the code.

Merci,
Marc
Posted By: matt_b Re: OCPD on secondary? - 11/22/09 02:19 AM
thanx for the input, we got the response on the RFI, now, they are goint to consider the primary protected by the breaker feeding it because it is within 50 feet, and visible, if two sets of doors remain open.

the secondary will be protected by a 1200A fusible disconnect that is 69"H, 18"D, and 36"W. this will be big enough for our 3- 3" Conduits with 4-500KCmil and 2/0 ground.

thanx again for the input.

matt
Posted By: ghost307 Re: OCPD on secondary? - 11/22/09 02:27 AM
The RFI response sounds like the designers investigated your question and found that they fouled up the design...and they're grasping at straws to avoid a big change order. Counting on 2 doors to be open so that you can consider something "in sight" as a real stretch that I wouldn't allow.

But; that being said, the RFI response has given you your marching orders and if it's later found to be wrong, it's THEIR liability.
Posted By: HotLine1 Re: OCPD on secondary? - 11/22/09 02:50 AM
Marc:
Yes, what you say is what I say. I just want to see if Scott has a methodology.

Posted By: renosteinke Re: OCPD on secondary? - 11/22/09 05:54 AM
You know, one thing missing from the NEC is any consideration of AIC and the influence the impedance of the transformer has on it.

The first point is that the transformer will limit the maximum current the secondaries will ever see. This can have a secondary effect of slowing the response of an OCPD on the primary side.

The second is that the downstream side may be eligible for less expensive, lower AIC-rated equipment, and lessened risk from arc-flash events.

I am becoming persuaded that there should always, as a matter of design, be some manner of OCPD on the secondaries for these reasons. Maybe not a 'main;' but at lugged panel with branch circuit OCPD would be fine.
Posted By: HotLine1 Re: OCPD on secondary? - 11/22/09 10:07 PM
Reno:

With the exception of one job, with one transformer, in my life as an EC, all transformer installs had OCP on primary and secondary. It was a matter of design and choice, mot NEC compliance.

The AIC of the secondaries is a calculation, I used and still do Bussmanns Point-to-point method.

Posted By: Scott35 Re: OCPD on secondary? - 11/26/09 04:31 PM
Hotline:

Quote

Scott:
Could you please explain the methodology for a MOCP of 1200 amp, on three (3) sets of 500KCmil, with 75 degree terminations. 500 KCmil Cu is 380 amps, which is compliant for 400 amp OCP. 2 sets would be compliant for 800 amp OCP, but 3 sets only total 1140 amps, and being >800 amps, a lower OCP is required, right?


Refer to Table 450.3(B), see note #1.

300 KVA Xformer - Secondary FLA (nom.) = 830 Amps.
Secondary Feeder Protection: 125% of FLA
Max. OCPD - Secondary Feeders: 1038 Amps.
Note #1 allows next higher OCPD rating, or 1200 Amps.

If the designed load from this Transformer was only 800 Amps, we could have used 3 sets of 400 MCM THHN CU. (335 Amps x 0.8 = 268 Amps; x 3 Sets = 804 Amps Max.), and still use the 1200 Amp OCPD for Secondary Feeder Protection.

I would not choose this design parameter, but it is compliant.
In fact, I would only choose the (3x) 500 MCM with 1200 Amp OCPD if the design LCL load was >80% of the Secondary FLA rating, and there were Motors > 5 HP started across the line from this Transformer (208V 3 Phase Motor > 16.7 FLA - 100.2 LRA).

Under normal design conditions, I would opt to use a 1000 Amp OCPD for the (3x) 500 MCM Secondary Feeders' Protection.

Quote

With the exception of one job, with one transformer, in my life as an EC, all transformer installs had OCP on primary and secondary. It was a matter of design and choice, mot NEC compliance.


I have designed + installed Transformers with OCPD for Feeders on both sides (Primary & Secondary), and for Primary Feeder Protection only - where the Secondary (SDS) is only One Voltage.
i.e. 480V x 240V 3Ø 3 Wire Delta...

When using Primary Feeder Protection only, the Primary Feeder's OCPD have been no more than 125% the rated Primary Current - as the only Transformers I have dealt with (design-wise or installed) were rated 9 Amps or larger.

If there is an advantage to run the Primary side "high", I will go with Primary + Secondary Protection - so the Primary Feeders may use an OCPD sized 250% the FLA.
Kind of like a Motor Circuit...

Quote

The RFI response sounds like the designers investigated your question and found that they fouled up the design...and they're grasping at straws to avoid a big change order.


I could imagine the environment around that EE Firm, when they reviewed the 1 Line -vs- the RFI!!!
After the initial "We can't be wrong" CYA statements ended, there would be a long series of "D'OHHH!!!" statements!!!

They (the EE Firm) should be greatful that the OP (matt b) caught this design issue and issued an RFI / RFC prior to performing the install per revised plan!

Currently there is one C/O (Change Order) for the original revisions,
then an addendum C/O for the revised-revisions wink

The C/O list could have been really painful! (for the EEs, not the EC!)

This post serves as a great example scenario to anyone in the field + Project Management & Designers.
In-depth review of ANY Electrical Design criteria should be done, so as to reduce Change Orders and impacting the Project Schedule.

This benefits the Client, which also benefits the Construction & Development teams (Electrical Contractor is part of C & D teams).

How much "fun" is it to submit a request for Change Order, and get approval to proceed within a few days!
Then to do so without impacting the critical path (Project's Schedule), due to the fact that the C/O issue likely will delay another trade by days / weeks / months!!!

Scott
Posted By: George Little Re: OCPD on secondary? - 11/26/09 07:18 PM
Nice post Scott. I would only add one comment that sometimes gets overlooked. When s transformer has Primary and Secondary protection and you are >9 amps., the protection is allowed to be 250% like you indicated. What gets missed is the sizing of the conductors feeding the Primary because the EE or the installer is only concerned with protecting the transformer. For example the Transformer could be rated at 100a. and you protect it at 250a. sometimes you are not protecting the primary supply conductors at their ampacity.