How are you handling your wet/dry bar countertop locations in dwelling units?
Wouldn't these counter top receptacles also need AFCI protection as well as GFCI protection for wet bars and all other receptacles within 6-foot from the edge if they are not considered as a kitchen or a similar area?
It appears that they can just be tied into any 15A general-purpose AFCI branch circuit or even on one of the 20A AFCI SABC's if located in a dinning room.

I think the NEC does a poor job addressing these now very common installations as this means that under counter refrigerators, wine coolers and other cord and plug connected counter top appliances like blenders, microwaves and toaster ovens could all share the same circuit as the other general-purpose receptacle loads in the rest of the room or even other rooms.

I feel that if they were considered as "similar areas", then at least they would be subject to the SABC requirements in 210.52,B,[1,2,3].