I would run 4 conduits, each containing 4 400MCM...A,B,C,N

For derating purposes, you use the 90deg column...so 400MCM is 380A x 4 = 1520A * 0.8 = 1216A

However, whether the Neutral is actually a CCC can be disputed. If not, then you can get away with 350MCM