I have a question about conductor sizing.
I have a 1200 amp main breaker on a 120/208Y service feeding a grocery store.
I came up with (4) 500 MCM per phase.
380A x4= 1520amps.
1520A x .80(T310.15(b)(2)(a)4-6 conductors in a raceway.=1216 A
1216A Round down to next standard= 1200A.

Have I gone astray somewhere? With all the lights, computers, etc. I would consider the neutral a current carrying conductor. I have seen other topics on here and none had mentioned the wire size I came up with.

As always thanks for the help gentlemen!
Gary