Ah! The labeling on that first diagram makes sense now.

As for the second, it appears to be a regular 3-way switching arrangement but with double-pole switching and thus four travelers.

It took me a while to figure out why anyone would need to do this, but I think I have an explanation.

Don't parts of Norway use a 220V IT system (i.e. neither pole is grounded) ?

Wiring a 3-way light this way would insure that when the switches are set for the light to be off that both poles on the lampholder are disconnected from the supply.