The 1996 language said the unreidentified white shall feed the switch in 200-7 Ex. 2.

But doesn't 2002 200.7(C)(1) allow the use of the reidentified "white" wire as a ungrounded conductor anyway? This would allow the use of the reidentified white as the switch leg to the fixture or as the traveller.

As I read 200.7(C)(2) I see a positive language statement reversing the 1996 and earlier exception that allowed the use of a cable's unreidentified white as the hot. (C)(2) says "where" the white is used to feed a switch loop. . .I don't pick up the "shall" pointing at anything but reidentification.

Help me see how I'm confusing myself.

Inquiringly,

Al