Posted By: mark wiring a three way switch - 07/28/02 05:05 PM
can i get a schematic to wire a three way switch?
Posted By: sparky Re: wiring a three way switch - 07/28/02 05:40 PM
<IMG SRC=\"https://www.electrical-contractor.net/ubb/smile.gif\">click me
Posted By: Matt M Re: wiring a three way switch - 07/28/02 09:18 PM
Sparky,

Re-identifying the white wire with black tape such as in the last diagram does not satisfy the requirement of article 200.7c2 does it? I believe the white wire must be re-identified, but it must be used as one of the travelers, and not as a return conductor from the switch to the light. Even though you've re-identified the wire with black tape, you still end up with both wires feeding the light being white. When the tape falls off sometime in the future, there will be no way to visually identify which wire is which.

Also, because the NEC requires the white wire to be "permentantly" re-identified, does taping it qualify as a permenant means? I know that many do it this way, but does it technically satisfy the NEC? I use a permenant tip magic marker to color the exposed ends. Matt
Posted By: Electra Re: wiring a three way switch - 07/29/02 03:37 PM
Good catch Matt. The white wire is not allowed to be used as the switch leg even though it is reidentified, just for the reason you stated. The white wire would be reidentified and used as one of the travellers. It is perfectely okay however to reidentify with tape.
Posted By: sparky Re: wiring a three way switch - 07/30/02 12:54 AM
LOL!, well Matt, you've caught me bettween an old link & the 02', very good.....

so, i would recommend that one end get fed, one gets switched, and the white remain neutral throughout...


probably cut the gauss down too!

[Linked Image]
Posted By: ElectricAL Re: wiring a three way switch - 07/30/02 03:44 AM
The 1996 language said the unreidentified white shall feed the switch in 200-7 Ex. 2.

But doesn't 2002 200.7(C)(1) allow the use of the reidentified "white" wire as a ungrounded conductor anyway? This would allow the use of the reidentified white as the switch leg to the fixture or as the traveller.

As I read 200.7(C)(2) I see a positive language statement reversing the 1996 and earlier exception that allowed the use of a cable's unreidentified white as the hot. (C)(2) says "where" the white is used to feed a switch loop. . .I don't pick up the "shall" pointing at anything but reidentification.

Help me see how I'm confusing myself.

Inquiringly,

Al
Posted By: sparky Re: wiring a three way switch - 07/30/02 10:05 AM
Al,
it is not worded well, and has been the source of much ado.

there has been much on this, i believe it was addressed in the 'Code Q of the Day' e-mailings, as well as Mike Holt's code updates in the trade mags.....

my personal feeling is that the NEC should not cater to dummies. this 're-identification' thing has flip-flopped through a number of code cycles.

if in fact there is some 'safety' aspect, i do not see it, as true trades(persons) would all know which is the 'hot' in a compliant installation of B & W to a s.p. switch...

besides, if you look at the HB illustration of 200.6(E) EX#1 you'll see white tape being applied to a black conductor in armored cable, no problem! , so i would not expect that 14-3,12-3 etc be run to all switch legs and pop up the box fill, make for an unused conductor, and create more confusion.....i haven't seen anyone wire in such a manner as yet......

methinks that this is somehow related to the colored NM marketing of late, and will continue being lobbied ( read the latest NEC digest lead article) for nothing but NM variations , totally profit driven.....

the 20.7 HB commentary here supplies some rationale ;

Quote
Previous editions of the Code permitted switch loops that contained a white insulated conductor that was used to supply the switch and that was not used to supply the luminaires to remain white. Prior to the 1999 NEC, re-identification of this particular ungrounded conductor was not required. However, many electronic automation devices requiring a grounded conductor are now available for installation into switch outlets. Therefore, re-identification of all ungrounded conductors that are white or any permitted white coloring is now required at each and every termination point. The required re-identification must be effective, permanent, and suitable for the environment, in order to clearly identify the insulated conductor as an ungrounded conductor. Proper re-identification should eliminate the possibility of miswiring new electronic automation devices during installation.

desends saop box.... [Linked Image]
Posted By: pauluk Re: wiring a three way switch - 07/30/02 05:43 PM
For anybody who cares, over here we usually use the black (normally neutral) as the return from switch to light and the red as the feed to the switch. Yes, it results in two black wires at the lamp (code requires the hot black to be reidentified red).

It is possible to buy NM-type cable with two red wires, but very rare to see it used.
Posted By: sparky Re: wiring a three way switch - 07/31/02 12:18 AM
which you do with tape Paul?

BTW...
someone here previously suggested drilling a small hole in the tip of a 'permanent' marker , thus compling with 'permanence'......

said dedication to the NEC is admirable, yet the NEC intent seems hazy.....
Posted By: sparky66wv Re: wiring a three way switch - 07/31/02 04:36 AM
Scott (electure) mentioned in another thread of the same ilk, that the chemicals is said marker may not be proven to be safe for thermoplastics or any other insulation type...

So is it better for the tape to fall off, or the ink to attack the insulation?

On side note:

I've had Scotch-kote soften the jacket on SOW cord that we were using for water fountain lights... I had put some Scotch-kote on where the SOW meets the WP connector gasket, and is softened the jacket rather badly.

Who'd a-thunk it?
Posted By: pauluk Re: wiring a three way switch - 07/31/02 09:52 AM
Quote

which you do with tape Paul?

Yes -- Either tape or a short length of red sleeving.
Posted By: Matt M Re: wiring a three way switch - 08/01/02 03:36 AM
Sparky66,

I've used the old standard black Sanford markers for years (way before it was an NEC requirement), and have never noticed any degradation of the insulation. I have however noticed on several occasions plastic electrician's tape where the adheasive has become gummy and the tape itself has become brittle and unraveled in just a few short years. I would think that the solvents that are used in some paints would be just as harsh as the inks used in marker pens, and the NEC specifically mentions painting as one of the effective means to permanently reidentify the conductor. I contend that when code making panel No. 5 decided to use the wording "permanent means", they meant permanent.

Sparky,

The requirement for the white conductor to only be used as a supply to the switch and not the return to the outlet was not new in "02". The oldest code book that I own is a 1975 edition, and its there in 200-7, exception #2 with no change bar in the margin along side, so it had to be a requirement even in the 1972 edition. In those days however, the NEC specifically added that reidentification for use in a 3 or 4-way circuit was not neccesary.

Granted, these are minor violations, but nonetheless they are violations.

Matt
Posted By: ElectricAL Re: wiring a three way switch - 08/01/02 04:45 AM
Boy, I still don't get it.

Here. . .string together the emphasized words of (C) with the emphasized words of (1), and second, string the emphasized words of (C) with the emphasized words of (2).

Quote
2002 200.7(C) Circuits of 50 Volts or More. The use of insulation that is white or gray or that has three continuous white stripes for other than a grounded conductor for circuits of 50 volts or more shall be permitted only as in (1) through (3).

(1) If part of a cable assembly and where the insulation is permanently re-identified to indicate its use as an ungrounded conductor, by painting or other effective means at its termination, and at each location where the conductor is visible and accessible.

(2) Where a cable assembly contains an insulated conductor for single-pole, 3-way or 4-way switch loops and the conductor with white or gray insulation or a marking of three continuous white stripes is used for the supply to the switch but not as a return conductor from the switch to the switched outlet. In these applications, the conductor with white or gray insulation or with three continuous white stripes shall be permanently re-identified to indicate its use by painting or other effective means at its terminations and at each location where the conductor is visible and accessible.

The supply to a switch, switch leg and travellers are all ungrounded conductors (except for some arcane K&T situations). Re-identify the white used in any of these and (C)(1) is satisfied.

(C)(2) is a special subset of (C)(1). The switch supply wire is ungrounded. (C)(1) has already told us to re-identify it if it is from a cable and it is white. But, just to make it crystal clear, (C)(2) describes the 1996 200-7 Ex. 2 and earlier practice where the "white" had to be the supply by the 1996 and older language.

By way of further, redundant, crystal clarity, the 2002 NEC Handbook says after 200.7(C)(2):

Quote
Therefore, re-identification of all ungrounded conductors that are white or any permitted white coloring is now required at each and every termination point.

This would allow the last threeway circuit diagram the Matt first talks about at the top of this thread to be correct as shown.

Al
Posted By: resqcapt19 Re: wiring a three way switch - 08/01/02 02:42 PM
Al,
I don't see (C)(2) as a special subset of (C)(1). In my opinion the intent of the code is that the white only be used as the supply to the switch, when part of a cable used for switch loops. The only change that was made in the '99 code was to require that the white when used to supply the switch be reidentified as a hot. In the earlier codes the reidentification was not required.
You use (C)(1) for cables that are mot part of switch loops where the white is not used as a grounded conductor. You use (C)(2) with cables used for switch loops and the white is used as the supply to the switch.
Don
Posted By: Matt M Re: wiring a three way switch - 08/01/02 04:04 PM
What Don said! LOL

(C)(2) is not a subset of (C)(1).

(1) and (2) are both subsets of (C), which is a subset of 200.7.

A good example of an application using (C)(1) is where a 2 conductor romex is used on a 240 volt branch circuit.



[This message has been edited by Matt M (edited 08-01-2002).]
Posted By: ElectricAL Re: wiring a three way switch - 08/01/02 05:07 PM
I must be really thick headed. Please bear with me. . .

Set one = All white wires in cable assemblies

Set two = cable assembly white wires used as ungrounded conductors

Set three = cable assembly white wires that are ungrounded that are used in switch loops

Set four = cable assembly white wires that are ungrounded that are used in switch loops only to supply the switch but not as a return from the switch to the outlet.

Set five = cable assembly white wires that are ungrounded that are used in switch loops as a traveller between 3ways and 4ways.

Set 1 contains all of 2, 3, 4 & 5
The part of Set 1 that is NOT 2, 3, 4 & 5 = plain old grounded conductors

Set 2 contains all of 3, 4 & 5

Set 3 contains all of 4 & 5

Set 4 & 5 do not intersect (can't use a supply as a traveller - except maybe in a california 3way).

Here's my point, cable assembly white wires that are ungrounded that are used in switch loops only to supply the switch but not as a return from the switch to the outlet (Set four) is completely contained inside the set of all cable assembly white wires used as ungrounded conductors (Set two).

Seems to me that (C)(2) is a subset of (C)(1), and both (C)(2 & 1) are subsets of (C), which is all white wires.
Posted By: ElectricAL Re: wiring a three way switch - 08/01/02 05:22 PM
Switch legs are ungrounded conductors.

Or to say it another way, if I don't set up my cables and their conductors in a switch loop with 3ways and 4ways so that the former white conductor is used only for the switch supply or the traveller, because I have re-identified the white conductors I can use them as ungrounded conductors to the end that I need, i.e., getting the light to work when I flip the switch.
Posted By: Matt M Re: wiring a three way switch - 08/01/02 07:08 PM
Electrical,

I guess I don't see what you're missing.

200.7(A) explains that the conductors as outlined in (1), (2), and (3) shall only be used as the grounded circuit conductor, UNLESS otherwise permitted in 200.7(B) & (C).

200.7(B) deals with circuits of less than 50 volts, and does not apply here.

200.7(C)(1) is just saying that where the conductors that were outlined in 200.7(A)(1), (2), and (3) are part of a cable assembly, and they are used as an ungrounded conductor, they must be permanently reidentified.

200.7(C)(2) is saying that where the conductors that were outlined in 200.7(A) (1), (2), and (3) are part of a cable assembly AND are used for a single pole, 3-way, or 4-way switch loop, that these conductors not only must be reidentified, but they must also only be used as the supply to the switch, and not the return from the switch to the outlet.

200.7(C)(3) deals with flexible cords, and does not apply here.

Another thought on the possible intent that code making panel #5 had when they included the term "permanent means" in the wording of 200.7.

Comparatively, lets examine the wording of 200.6(B), where conductors of sizes larger than #6 are used as a grounded conductor.... sort of the reverse in effect (use of white tape IS and has long been an acceptable means here).

Nowhere in this section does it use the term "permanent means". It only requires that at the time of installation, the conductor be identified by a "distinctive white marking" at its terminations. Matt
Posted By: ElectricAL Re: wiring a three way switch - 08/01/02 09:01 PM
Thanks Matt,

How's the weather by the Lake? It's drying out nicely down here.

I don't see what I'm missing yet, either.

Quote
1996 NEC 200-7. Use of White or Natural Gray Color. A Continuous white or natural gray covering on a conductor or a termination marking of white or natural gray color shall be used only for the grounded conductor.

Exception No. 1: An insulated conductor with a white or natural gray finish shall be permitted as an ungrounded conductor where permanently re-identified to indicate its use, by painting or other effective means at its termination, and at each location where the conductor is visible and accessible.

Exception No. 2: A cable containing an insulated conductor with a white or natural gray outer finish shall be permitted for single-pole, 3-way, or 4-way switch loops where the white or natural gray conductor is used for the supply to the switch, but not as a return conductor from the switch to the switched outlet. In these applications, re-identification of the white or natural gray conductor shall not be required.

Ex. 3 & Ex. 4 don't pertain at the moment.

200-7 by itself, not looking at the exceptions, hypothetically, says the white or gray can only be used as a grounded conductor. (That's in raceways, cables, cords, whatever, no limits are posted on the statement.)

Adding Exception 1 modifies the blanket statement of 200-7 by allowing a white or gray to be used as an ungrounded conductor when it is re-identified. Now, if this is where section 200-7 ended, we would've been always re-identifying the white in a cable assembly whether used in a switch loop or not. (Again, this Exception applies in raceways, cables, cords, whatever.)

Adding Exception 2 modifies both 200-7 and 200-7 Ex 1 together by allowing cable containing a white or natural gray conductor not to be re-identified when installed as described. This is the exception for the exception. IMO. As long as I carefully install the white, I don't have to re-identify it. I can re-identify it if I wish to take the time. If I re-identify the white wire, I am complying with exception 1. I "shall be permitted" to not re-identify. Notice that Ex. 2 doesn't say "I shall not re-identify". Re-identification "shall not be required" is totally different than: Re-identification shall not be done."

You know? As I get into this I don't even see where 1996 requires a re-identified white in a cable to only connect as the supply for a switch. The option to not mark the white is given when it comes from a cable and is installed in certain places in the switch loop. That's all.

Fascinating.

Sorry for the length. I got wound up. Mmmm, strong coffee is Good coffee.

Al
Posted By: ElectricAL Re: wiring a three way switch - 08/01/02 10:25 PM
OK. I just chased the language back to 1956.

From 1975 through 1996 the language doesn't change except in 1987 where "outlet" in 200-7 Ex 1 is changed into "location".

Other than that one word, 200-7, 200-7 Ex 1 and 200-7 Ex 2 don't change until way back in the 1971 NEC.

And it's an interesting change. Note: "identified" = grounded, and "unidentified" = ungrounded.

In 1971 200-7 Ex 2 has a fine print note. Here's the thing in it's total:
Quote
200-7. Identified Conductor in Grounded Circuits Only. Conductors having white or natural gray covering shall not be used other than as conductors for which identification is required by Section 200-2, except under the following conditions, and then only where they are, in other respects, suitable for use as ungrounded conductors in the circuit:

Exception No. 1: Identified conductors, rendered permanently unidentified by painting or other effective means at each outlet where the conductors are visible and accessible, may be used as unidentified conductors.

Exception No. 2: Cable containing an identified conductor may be used for single-pole, 3-way or 4-way switch loops where the connections are so made that the unidentified conductor is the return conductor from the switch to the outlet.


FPN: This exception makes it unnecessary to paint the terminal of the identified conductor at the switch outlet.

This FPN is the same back in the '56 NEC.

Seems clear to me the CMP's intent was to save sparky a bit of labor when installing switch loops, rather than restrict the use of the re-identified white to supply of switch only.

Al

[This message has been edited by ElectricAL (edited 08-01-2002).]
Posted By: Matt M Re: wiring a three way switch - 08/01/02 11:13 PM
Hi again electrical,

The weather has been great here, however because of all of these lakes, the mosquitoes have been hell! LOL I know what you mean about strong coffee being good coffee.

Well I guess I can only add that it seems clear to me that the evolution of 200.7 into requiring the reidentification of the white conductor was an attempt to further eliminate confusion, and was in addition to the long standing requirement that it only be used as the supply to the switch.

To the untrained person, white wire = neutral = safer to touch. When a trained person sees a white wire connected to the terminal of a switch, he knows that it is probably not a neutral, whereas the untrained person still may see a neutral. I believe that this is the reason that CMP #5 added the requirement to reidentify.

It is obvious to me why they wanted the return conductor to be black. You have a choice of two conductors, a black and a white. Since one conductor is no more or less difficult to use than the other, why not use the black as the return so that at that outlet you have a black hot, and a white neutral? If the white wire were truly reidentified along its entire exposed length at all splice locations it may not be a problem, but a small strip of tape could be overlooked or may not mean anything to an untrained person. A mixup here would reverse the polarity on a lampholder or receptacle, whereas from a safety standpoint it doesn't matter if the wires are reversed on a switch. Matt

[This message has been edited by Matt M (edited 08-01-2002).]
Posted By: Sean WB Re: wiring a three way switch - 09/16/02 03:41 AM
reason they are more partial (I think) to using a white wire for a feeder to the switch rather than to the fixture is because the fixture will more likely be replaced/upgraded etc.
Taping the switched hot (white) with red or black is acceptable here in the south.
Note that you have to refer to your local jurisdictions as well.
Posted By: George Re: wiring a three way switch - 09/16/02 06:03 AM
I believe that 200.7(C) (1) and (3) are connected with OR not AND.

This allows either the white (re-identified) or black to be used as the ungrounded conductor to the switch. And either to be ungrounded as the power returns from the switch.

I guess that the NEC has a process to resolve these questions.
Posted By: engy Re: wiring a three way switch - 09/20/02 06:21 PM
“In my opinion the intent of the code is that the white only be used as the supply to the switch, when part of a cable used for switch loops.”

I do not think that is the intent.

C2 is saying WHERE the white is used for the supply…
I remember way back when being told that if you use the white for a supply to a switch, you don’t need to re-identify it because it is spliced to a black (or red) conductor. I think C2 just specifically addresses this mindset.

C1 will allow you to use the white as a traveler if re-identified.
Posted By: ElectricAL Re: wiring a three way switch - 09/21/02 04:09 AM
Welcome, Engy!

What about using a re-identified white conductor as a switched leg back to the luminaire?

Al
Posted By: sparky Re: wiring a three way switch - 09/21/02 11:08 AM
yes, welcome engy !


in reference to this 'permanent' deal,

there are some who would insist on running 14-3, 12-3 switch legs, with the white unused.

Perhaps the NEC has assessed DYI confusion in viewing two wires in a box with switch?
[Linked Image]

other than that i cannot see any safety relation this code controversy would address.....
Posted By: Scott35 Re: wiring a three way switch - 09/28/02 09:56 AM
Mark (and anyone else needing Schematics for 3 and 4 way Switchloops), I have recently included Schematics to the ECN Technical Reference area, which should be of help to you.

These Schematics can be accessed by either:
Using this Hyperlink:
3 way and 4 way Switchloop Schematics

Or one of the following methods:

<OL TYPE=1>

[*]Going to the Tech. Reference area and using the "Menu",

[*]Selecting the topic from the Tech. Reference area's main page.
</OL>