Here's a reply I received from Bussmann:

Quote
Hi Joe,

It appears one of the members properly identified the product which we offer.

We offer "dummy" fuses or neutrals for Class H/R, Class CC, midgets (13/32" X 1-1/2") and small dimension (1/4" X 1-1/4") fuses.

These fuses can only be utilized where overcurrent protection is not required by the code, such as for neutrals.

For example, let's say you have a 120/240V system and use a 3 pole 240V switch.

You could run the two hot phases through two of the poles with protection by a fuse and install the "dummy" fuse in one pole, and run the neutral through.

They also use these allot in lighting circuits for the neutral conductor.

Bussmann


Joe Tedesco, NEC Consultant