#99768 - 09/04/06 11:10 PM What is 225.38(C) trying to say  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,099
Estero,Fl,usa
Why should you need to disconnect the grounded conductor?


Greg Fretwell

2017 / 2014 NEC & Related Books and Study Guides

#99769 - 09/05/06 05:12 AM Re: What is 225.38(C) trying to say  
Happy Birthday iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
You might want to pull it for testing purposes.

If you are looking for illegal ground to neutral connections lifting the neutral would be step one along with the MBJ.

That said I don't understand what it really accomplishes, I have never seen any one in the field talk about it. It seems more of a construction specification of service rated equipment. 225.36

Now when we use the exception to 225.36 do we need to use two pole snap switches so we can break both grounded and ungrounded conductors simultaneously?

FWIW 225.38(C) mirrors 230.75


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#99770 - 09/05/06 07:22 AM Re: What is 225.38(C) trying to say  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,260
Fullerton, CA USA
We've got a couple of jurisdictions here in SoCA that have you perform a "neutral to ground" continuity test (with the link removed) at final inspection.
This way they can verify that there are no grounding connections on the neutral anyplace but where they belong....At the service.
Resi services are done with the individual neuts disconnected from the neutral bar.

A good idea, IMO



Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.002s) Memory: 0.7521 MB (Peak: 0.8754 MB) Zlib enabled. Server Time: 2017-07-21 00:28:58 UTC