New Grounding Methods ??? #99329
10/28/04 06:06 AM
10/28/04 06:06 AM
M
Megawatt  Offline OP
Member
Joined: Mar 2004
Posts: 76
Lexington,Ky, USA
Just got My 2005 Code Book, looking at some changes, & it seems We are going to have some issues with grounding rebar in concrete.
Does anyone have any ideas on this yet, Would it be possible to have the concrete contractors leave a section stubed out above the pour ?
On jobs where there aren't any conduit runs to be incased, the EC may not be anywhere near the site when the pour occurs.
Also, it looks like Building Steel, Rebar, Metal Waterline etc will ALL be connected now.

2017 / 2014 NEC & Related Books and Study Guides
Re: New Grounding Methods ??? #99330
10/28/04 08:18 AM
10/28/04 08:18 AM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
I think what will have to happen is that if the EC isn't on site before or during the pour, the footing contractor will have to stub out a piece of rebar for the EC to tie onto. As far as the building steel, water line, etc., these were already required to be tied together.

I better make sure we're on the same page. You're talking about 250.50, right?

[This message has been edited by Ryan_J (edited 10-28-2004).]


Ryan Jackson,
Salt Lake City
Re: New Grounding Methods ??? #99331
10/28/04 08:53 AM
10/28/04 08:53 AM
M
Megawatt  Offline OP
Member
Joined: Mar 2004
Posts: 76
Lexington,Ky, USA
I believe so, I don't have My Code book with Me, but I think that is correct.
What do You know about the coated rebar ???
That doesn't require bonding ??

Re: New Grounding Methods ??? #99332
10/28/04 10:58 AM
10/28/04 10:58 AM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Coated rebar is commonly used in bridge construction and has no metal contact with the concrete.

I have never seen it used in footers, but doesn't mean it isn't.

Roger

Re: New Grounding Methods ??? #99333
10/28/04 03:08 PM
10/28/04 03:08 PM
M
Megawatt  Offline OP
Member
Joined: Mar 2004
Posts: 76
Lexington,Ky, USA
Our Cont Ed Instructor said it may be used more often, After 2005 is adopted, if the cost isn't too prohibitive.
Seems easy enough to just stub up a piece above the pour though....

Re: New Grounding Methods ??? #99334
10/28/04 04:28 PM
10/28/04 04:28 PM
R
Ryan_J  Offline
Moderator
Joined: Aug 2003
Posts: 1,374
West Jordan, Utah, USA
The cost of epoxy coated steel, in my opinion, is never going to be less expensive than simply using normal steel and having to use it as an electrode.


Ryan Jackson,
Salt Lake City
Re: New Grounding Methods ??? #99335
10/28/04 06:41 PM
10/28/04 06:41 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
The beauty when using the rebar as a grounding electrode is that the 2 ground rods are no longer required.
Also, just because the 2005 NEC is out, doesn't mean that your town or state has adopted it.


Earl
Re: New Grounding Methods ??? #99336
10/29/04 01:23 PM
10/29/04 01:23 PM
C
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
Now that it is going to be required everywhere . . . eventually. How does Florida do it now? I believe they require the Ufer throughout the state and the concrete contractor just turns up a piece of the rebar in the area of the service. I would like to hear how it's done in Florida now. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy
Re: New Grounding Methods ??? #99337
12/22/04 12:19 AM
12/22/04 12:19 AM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
They turn up a #5 in SW Florida. It comes up into the block cell and they knock a hole so the can get to it (usually sprayed green so it doesn't get poured solid when they do the dowels). The electrician pushes his #4 down from the panel to meet the #5, puts a bronze acorn on it and puts a blank cover over the hole.


Greg Fretwell
Re: New Grounding Methods ??? #99338
12/30/04 08:58 AM
12/30/04 08:58 AM
G
Gary S  Offline
Member
Joined: Dec 2004
Posts: 12
Houston, Texas, USA
It is my opinion that the intent of previous editions of the code was that the rebar system was supposed to be used as a portion of the grounding electrode already. The 2005 change from "If available on the premises" to "that are present at" is simply an effort to more concisely spell out what the intent was. There is nothing new here. We should have been connecting into the rebar system all along.

Page 1 of 4 1 2 3 4

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
JoeKP
JoeKP
Berkley, MA
Posts: 144
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,587 Are you busy
180,382 Re: Forum
170,859 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.018s Queries: 15 (0.004s) Memory: 1.0252 MB (Peak: 1.2025 MB) Zlib enabled. Server Time: 2018-01-22 02:20:53 UTC