#98501 - 12/30/04 09:52 PM Ground rod & water main  
ToHo  Offline
Member
Joined: Dec 2004
Posts: 46
N.Y.
Hi... Just wanted some feed back on installing 2 ground rods for a residential service instead of 1 ground rod and the water main. Speaking with a inspector here in Rochester NY , he said they would prefer to see 2 ground rods. That was new to me.. anybody have a opinion on this subject... thanks ToHo


2017 / 2014 NEC & Related Books and Study Guides

#98502 - 12/30/04 10:20 PM Re: Ground rod & water main  
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
Please read 250.50. It requires the water piping system to be used as a grounding electrode (assuming it is in contact with the earth for 10 ft or more) and another grounding electrode. If the additional grounding electrode is a driven electrode, a maximum of 25 ohms must be met or a second one must be driven no closer than 6 ft to the first one. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy

#98503 - 12/30/04 10:59 PM Re: Ground rod & water main  
ToHo  Offline
Member
Joined: Dec 2004
Posts: 46
N.Y.
Thanks charlie... I agree 100%. Its always nice to get another view. If a well is used on the premise w/ pvc piping into the house. Would you use 2 ground rods or could you use only one if the ohms reading was acceptable?


#98504 - 12/31/04 01:42 AM Re: Ground rod & water main  
Gary S  Offline
Member
Joined: Dec 2004
Posts: 12
Houston, Texas, USA
You would be compliant with only one rod as long as the resistance is less than 25 ohms. Also, even though the waterpipe from the well is PVC, if the water system in the house is metallic, then it must still be bonded to the service. Not as an electrode, but to make it the same potential as the equipment grounds.


#98505 - 12/31/04 09:53 AM Re: Ground rod & water main  
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
Gary, I agree completely. [Linked Image]


Charlie Eldridge, Indianapolis Utility Power Guy


Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,259
Joined: December 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7674 MB (Peak: 0.9065 MB) Zlib enabled. Server Time: 2017-04-25 04:42:48 UTC