Ground rod & water main #98501
12/30/04 08:52 PM
12/30/04 08:52 PM
T
ToHo  Offline OP
Member
Joined: Dec 2004
Posts: 46
N.Y.
Hi... Just wanted some feed back on installing 2 ground rods for a residential service instead of 1 ground rod and the water main. Speaking with a inspector here in Rochester NY , he said they would prefer to see 2 ground rods. That was new to me.. anybody have a opinion on this subject... thanks ToHo

2017 / 2014 NEC & Related Books and Study Guides
Re: Ground rod & water main #98502
12/30/04 09:20 PM
12/30/04 09:20 PM
C
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
Please read 250.50. It requires the water piping system to be used as a grounding electrode (assuming it is in contact with the earth for 10 ft or more) and another grounding electrode. If the additional grounding electrode is a driven electrode, a maximum of 25 ohms must be met or a second one must be driven no closer than 6 ft to the first one. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy
Re: Ground rod & water main #98503
12/30/04 09:59 PM
12/30/04 09:59 PM
T
ToHo  Offline OP
Member
Joined: Dec 2004
Posts: 46
N.Y.
Thanks charlie... I agree 100%. Its always nice to get another view. If a well is used on the premise w/ pvc piping into the house. Would you use 2 ground rods or could you use only one if the ohms reading was acceptable?

Re: Ground rod & water main #98504
12/31/04 12:42 AM
12/31/04 12:42 AM
G
Gary S  Offline
Member
Joined: Dec 2004
Posts: 12
Houston, Texas, USA
You would be compliant with only one rod as long as the resistance is less than 25 ohms. Also, even though the waterpipe from the well is PVC, if the water system in the house is metallic, then it must still be bonded to the service. Not as an electrode, but to make it the same potential as the equipment grounds.

Re: Ground rod & water main #98505
12/31/04 08:53 AM
12/31/04 08:53 AM
C
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
Gary, I agree completely. [Linked Image]


Charlie Eldridge, Indianapolis Utility Power Guy

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
sparky 16
Potseal 15
Popular Topics(Views)
243,589 Are you busy
180,383 Re: Forum
170,860 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.019s Queries: 14 (0.003s) Memory: 0.9660 MB (Peak: 1.1046 MB) Zlib enabled. Server Time: 2018-01-22 06:27:10 UTC