#98264 - 05/19/06 08:36 AM Fire stop/Draft stop  
Reel-Break  Offline
Member
Joined: Apr 2002
Posts: 178
nc
Hey seems where ever we wire there`s different standards for sealing the holes.I`m being told now the wiring holes must be ansi #### fire rated red type fire stop.I is there a standard or something that will clarify this. The plumber used something else??I`m trying to save some dollars as the red is much more expensive.I also picked up all my little scrap copper.Man its getting unreal roll 14/2 255.00 yesterday.250` roll 12/2 106.00


2017 / 2014 NEC & Related Books and Study Guides

#98265 - 05/19/06 07:17 PM Re: Fire stop/Draft stop  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
You are not "required" to use any particular method; you are required to maintain the integrity of the wall- that is, not make it less effective in blocking fire.

One may do this by simply using methods essentially the same as the original construction; for example, a hole in a brick wall can be patched with brick and mortar.

The 'red stuff' came about for two reasons:
The first was because the use of a flammable expanding foam resulted in a fire that darn near destroyed a nuclear reactor.
The second was because of the difficulty of telling a good patch from a bad one. For example, a wall with an inch of sheetrock needs for patches to also be an inch thick- not just a skim of plaster over a bit of tape. The red stuff is much easier to push into the opening, and (usually) expands to fill gaps when it gets hot.

Various fire-stop materials are rated by UL. Many of these listed products are little different from plaster or mortar. With any of them, it is essential that they be applied as the design specifies.
UL does publish a three-volume "Fire Resistance Directory." These designs are detailed there.



Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7444 MB (Peak: 0.8623 MB) Zlib enabled. Server Time: 2017-07-26 22:39:55 UTC