#98171 - 05/11/06 08:48 AM To bush or not to bush PVC  
Reel-Break  Offline
Member
Joined: Apr 2002
Posts: 178
nc
Hey guys whats everyone`s interp of 352.46 then refer to 300.4f Here`s the deal wired mobil home pvc male adapter sch 80 pvc well I failed because no bushings on the pvc male adapters.Are they required in this situation? Using 4/0 quad cable direct burial. Thanks waiting for inspector to call us now as he left no reference yesterday.


2017 / 2014 NEC & Related Books and Study Guides

#98172 - 05/11/06 09:05 AM Re: To bush or not to bush PVC  
ghost307  Offline
Member
Joined: May 2005
Posts: 902
Chicago Illinois USA
PVC may be non-conductive, but its edges are still sharp enough to damage insulation.
I think that's the reason behind 300.5H.
BTW, I always call for metallic elbows in underground PVC runs because the rope that pulls in the conductors can grind an edge in a PVC elbow during a tough pull. I've had cables fail to each other on an U/G feeder for just that reason before I adopted that little trick.


Ghost307

#98173 - 05/11/06 10:45 AM Re: To bush or not to bush PVC  
Reel-Break  Offline
Member
Joined: Apr 2002
Posts: 178
nc
Hey no rope here. Dug 10 ft ditch sch 80 down from box to proper depth direct burial cables to other end pvc to box slide wires in. But pvc fittings are beveled smooth and I don`t see how they can damage the wiring.


#98174 - 05/11/06 02:31 PM Re: To bush or not to bush PVC  
giddonah  Offline
Member
Joined: Jun 2005
Posts: 49
UT
Did he tell you exactly what point he was concerned with? Yes, the fittings are smooth, but when you cut a piece to length, the end isn't so smooth. Is there a point where wires exit through such an opening?


#98175 - 05/11/06 02:38 PM Re: To bush or not to bush PVC  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,080
Estero,Fl,usa
You might be able to make a case that the burred end of a PVC pipe you cut with a chain saw could damage conductors but if this is the threaded end of a PVC male adapter, I don't see the issue. They are as smooth as the edges of a plastic bushing.
Both are mass produced injection molded plastic. The chance of a flaw in the process that leaves a rough edge is about the same for either.


Greg Fretwell

#98176 - 05/11/06 03:33 PM Re: To bush or not to bush PVC  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
I am very doubtful that a PVC male adaptor provides a "smoothly rounded insulated surface" as discribed in 300.4(F) and would red tag the job without even hesitating. I'm comparing it to a female adaptor with a chase nipple or a threaded hub or boss that is an integral part of an enclousure. Sorry gentlemen.


George Little

#98177 - 05/11/06 05:16 PM Re: To bush or not to bush PVC  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,080
Estero,Fl,usa
OK "the code" has spoken, (we should fail it)now has anyone actually seen a conductor damaged by a PVC fitting?


Greg Fretwell

#98178 - 05/11/06 06:42 PM Re: To bush or not to bush PVC  
frenchelectrican  Offline
Member
Joined: Feb 2003
Posts: 939
Wi/ Paris France { France for ...
I hate to step in this one,,,


unforetally yes i did see few conductors got damaged by male termal adpator espcally after hard pull i did nick few of them [ugh !! ]

but the code required the bushing on the male adpator it been like that way for pretty long time i was not sure when it was enforeced.

I think it was debated before related with mobile home service hook up and kinda pretty common to get red flagged from this one if not carefull with bushing

Merci, Marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


#98179 - 05/11/06 06:48 PM Re: To bush or not to bush PVC  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Quote
352.46 Bushings
Where a conduit enters a box, fitting, or other enclosure, a bushing or adapter shall be provided to protect the wire from abrasion unless the box, fitting, or enclosure design provides equivalent protection.

I think that a male adapter requires a bushing based on this section.
Don


Don(resqcapt19)

#98180 - 05/11/06 11:05 PM Re: To bush or not to bush PVC  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,080
Estero,Fl,usa
I looked at a few fittings and I agree. For some reason <Carlon> makes the edge sharper than it has to be, perhaps to sell more bushings. It would be quite easy to make the edge rounded to provide "equivilent protection"


Greg Fretwell

Page 1 of 3 1 2 3

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 15 (0.004s) Memory: 0.8190 MB (Peak: 0.9935 MB) Zlib enabled. Server Time: 2017-05-25 06:48:21 UTC