Section 310.15(B)(20(a) requires derating of more than 3 current carrying conductors in a cable or raceway. Section 240.4(B) allows the next higher standard overcurrent device rating above the ampacity of the conductors being protected to be used. Does that mean I can bundle 40 14/2 NM cables together for long distances, and connect each to a 15 amp cb? 80 current carrying conductors would require a 35% derating from 25 amps to 8.75 amps. Can I then bump the cb up to 15 amps because Section 240.6 gives me the lowest standard rated breaker as 15 amps? Or, am I required to use a 10 amp fuse?
Earl
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
IMO you could use the next standard size listed (15 amp) on any of the circuits that are not multioutlet branch circuits supplying receptacles for cord-and-plug-connected portable loads.
Of course the ampacity of the cables would still be only 8.75 amps and the connected load could not exceed that.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Dec 2003
Posts: 751
OP
Member
|
So, if we combine my two posts, using luminaires that do not draw more than 2 amps, I could get away with that scenenario?
12 current carrying conductors require a deration of 50%, 50% of 25 aamps is 12.5 amps. Dividing by six luminaires, gives me 2.08333 amps each.
Earl
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Cool questions. IMO yes, 240.4(B) applies to the circuit as conditions (1), (2) and (3) are met and it tells us clearly "The next higher standard overcurrent device rating" a couple of times. 240.6 Standard Ampere Ratings shows the smallest standard rating as 15. Bob
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
I'm giving you guys a red sticker. Wording in the code is the "next higher standard overcurrent device" Not the next size circuit breaker. 10a. is the next size overcurrent device for earlydean's post. Guess someone is installing fuses on these circuits.
George Little
|
|
|
|
Joined: Jan 2001
Posts: 1,044
Member
|
I think that sticker should be pink instead of red, thereby giving partial credit. After all, Iwire did point out that going up to the next OCPD does not allow you to increase the ampacity (or load) of the conductors and he did correctly make the call about multioutlet circuits. These points seem to be lost on many, at least here in the Mountain State.
Few things are harder to put up with than the annoyance of a good example.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Interesting, I have to agree with you George, that is what it says. That aside I am not convinced the NEC intends to force the use of a fuse over a breaker. Bob BTW I will happily take a RED tag over a pink tag. Pink is the color of the spare hardhats for those that always misplace their own.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Dec 2003
Posts: 751
OP
Member
|
It takes a real manly man to wear a pink hardhat on a construction job!