#97692 - 03/14/06 08:51 PM Grounding/bonding 2 panels, 1 meter  
Trick440  Offline
Member
Joined: Aug 2005
Posts: 248
Waterford, MI, USA
Just wondering if theres an easier way.

I have a 400amp (300 maybe?) meter can with dual lugs to feed 2 200 amp main breaker panels.

So for the ground I come from each panel and run #6 to the ground rods. Thats fairly standard.

Now for the water main bond (or is it SEC?) I have ussually been running #4 from each panel to the water main.

Is there an easier way to do this? Can I just pull #4 from 1 panel to the water main, then pull a #4 jumper from that panel to the other?


Shake n Bake

2017 / 2014 NEC & Related Books and Study Guides

#97693 - 03/15/06 09:19 AM Re: Grounding/bonding 2 panels, 1 meter  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 831
Michigan
400 amp service requires 500 mcm =380 amps at 75%. go to 250.66 a 500 requires a 1/0 copper grounding electrode conductor.
you can run a 1/0 to the ist panel then (TAP)a #4 from (OUTSIDE) the panel to the second panel.You cannot Splice (unless Cadweld or Listed compression ) and going in one panel to the Neutral bar then to the other would be like a splice , But you can Tap.(250.64d)Page 214 of the NEC 2005 Handbook shows a nice detail of this.Since a #6 copper) per 250.66(A) is the largest size wire required to a Ground rod no matter what the size service. I feel you could run one #6 from the Ground Rod or Rods to the Water line (Detail on page 215 NEC Code Handbook) and you;d be done.All of theses are also shown well in Soares Grounding book.


#97694 - 03/15/06 03:59 PM Re: Grounding/bonding 2 panels, 1 meter  
markp  Offline
Member
Joined: Apr 2004
Posts: 60
Kent, WA, USA
As long as the neutrals between the panels and the meter are 1/0 copper or 3/0 aluminum or larger, you don't need to run a ground tap between panels (but you can if you want to).

Just run a 1/0 copper (or maybe a #2 copper -- depends on the size of service entrance conductors actually used) from one panel to the water pipe. Ideally, from that same panel, run a #6 copper to your first ground rod and then a #6 bonding jumper from that rod to the next.

[This message has been edited by markp (edited 03-15-2006).]


Mark
Kent, WA

#97695 - 03/15/06 06:02 PM Re: Grounding/bonding 2 panels, 1 meter  
Trick440  Offline
Member
Joined: Aug 2005
Posts: 248
Waterford, MI, USA
Ok let me get this straight...

I only need to run 1 #6 ground wire, from 1 panel, to the ground rod. So I don't have to do that on both panels?

I think I understand about the 1/0 needs to come from only 1 panel, and hit the water pipe. We have been doing the 2 runs of #4 copper forever. <--- is the 2 runs wrong?

thanks for the help.


Shake n Bake

#97696 - 03/17/06 12:10 AM Re: Grounding/bonding 2 panels, 1 meter  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Trick440, what you are doing, is kinda allowed depending on how you look at it... This has been argued here before, contensiously.....

It is allowed by 250.64D depending on how you look at it... The way I see it there should only be one conductor, and full sized on the electrode, unless both are exothermically welded to it. As it says the conductor shoud be "without a splice". Otherwise one could be removed, and you would have a single 1/2 sized conductor serving as the GEC. 2 connections at the rod or water serve as a splice in what should be a single full sized conductor IMO. It says conductor, singlular....


Mark Heller
"Well - I oughta....." -Jackie Gleason

#97697 - 03/17/06 04:50 PM Re: Grounding/bonding 2 panels, 1 meter  
markp  Offline
Member
Joined: Apr 2004
Posts: 60
Kent, WA, USA
I think not having all those smaller parallel grounds makes more sense when you realize you could connect your ground electrode in the meter can (if the POCO permits that) or anyplace along the service neutral (at the weatherhead even). NEC 250.142 allows the service neutral to be the wire you ground all your service equipment with as long as the neutral is sized per 250.66 or larger.

Having ground taps clouds the issue for me, but you would need to do that if you have a panel with no neutral.


Mark
Kent, WA


Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013