03/09/06 05:43 PM
03/09/06 05:43 PM
T
Tim Peters  Offline OP
Member
Joined: Mar 2003
Posts: 10
517.80 of the NEC states:

Equivalent insulation and isolation to that required for the electrical distribution systems in patient care areas shall be provided for communications, signaling systems, data system circuits, fire alarm systems, and systems less than 120 volts, nominal.

FPN: An acceptable alternate means of providing isolation for patient/nurse call systems is by the use of nonelectrified signaling, communications, or control.

Would this mean all low voltage in a accessible drop ceiling located over a patient care area would need to be in EMT or FMC? And by insulation do they mean a literal interpretation ie; THHN THWN?

Any input would be appreciated, thanks

2017 / 2014 NEC & Related Books and Study Guides
Re: Low Voltage in patient care ceilings #97635
03/09/06 11:48 PM
03/09/06 11:48 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,167
Estero,Fl,usa
The short answer is yes.
There may be some mitigating factor somewhere but I always saw THHN in pipe for nurse calls and such.


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
Potseal 15
sparky 15
Popular Topics(Views)
243,595 Are you busy
180,393 Re: Forum
170,863 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.013s Queries: 14 (0.004s) Memory: 0.9413 MB (Peak: 1.0545 MB) Zlib enabled. Server Time: 2018-01-22 22:19:36 UTC