#96178 - 11/08/05 07:27 PM Buried box V. Buried splice  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
We know that splices in j-boxes must remain accessible.
What about a section of NM cable that was used to feed a range hood and is now capped off in a wall case with a blank cover, with an undercabinet microwave installed in front of it.
Or, for that matter, what about any box that has a circuit that is dead ended (no splices), blanked and spackled over?


2017 / 2014 NEC & Related Books and Study Guides

#96179 - 11/08/05 07:42 PM Re: Buried box V. Buried splice  
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
So long as the circuit remains de-energized at the source, I see no problem. I would cut the wires out of the panel just to be sure no one re-connects them at a future date. Or, at least, identify the wires in the panel with an attached note detailing where the other end of the circuit is.


Earl

#96180 - 11/08/05 10:55 PM Re: Buried box V. Buried splice  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Thanks early,

I'm talking about live wires that are fed from an unknown point. The box would be obscured by a microwave, but it does not contain a splice, just dead-headed wires. I'm interested in code references, please.


#96181 - 11/09/05 11:53 AM Re: Buried box V. Buried splice  
sabrown  Offline
Member
Joined: Dec 2002
Posts: 302
Ogden, Utah, USA
314.29 - "wiring ... rendered accessible without removing any part of the building"

The definition in article 100 does not clarifiy this either. It would be easy to say the microwave is just an obstacle thus rendering the box not "readily accessible."

So the question is does the AHJ consider a pemenantly mounted microwave part of the building?

I could stretch things and say if typically the appliance is permently mounted and goes with the building when sold, that it is part of the building. But, that is a call for the AHJ in this case.

Shane


#96182 - 11/09/05 11:57 AM Re: Buried box V. Buried splice  
sabrown  Offline
Member
Joined: Dec 2002
Posts: 302
Ogden, Utah, USA
By the way spackle is part of the building, thus the last question is a clear violation of 314.29. See definition of accessible dealing with finish removal.


#96183 - 11/09/05 01:10 PM Re: Buried box V. Buried splice  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,097
Estero,Fl,usa
Equipment is not building finish, otherwise you couldn't hang a luminaire.


Greg Fretwell

#96184 - 11/09/05 02:40 PM Re: Buried box V. Buried splice  
Dnkldorf  Offline
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
That ain't what the guy at Home Depot told me [Linked Image]


Dnk....

[This message has been edited by Dnkldorf (edited 11-09-2005).]


#96185 - 11/09/05 11:28 PM Re: Buried box V. Buried splice  
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
In my humble opinion, even a kitchen cabinet can be removed; I've done it plenty of times. To me, as long as the building finish doesn't cover the box, it's accessible, although not readily accessible.

Ideally, it would be better to find the other end of this section of cable and disconnect it, but it's not mandantory.


Larry Fine
Fine Electric Co.
fineelectricco.com


Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.7923 MB (Peak: 0.9547 MB) Zlib enabled. Server Time: 2017-07-20 16:43:47 UTC