#95505 - 09/16/05 11:30 PM Fixture Canopy Fill  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Looking at 410.10 I conclude that the canopy of a luminaire is only suitable for luminaire wires and there connecting devices. How much branch circuit conductor is permitted in the canopy?


George Little

2017 / 2014 NEC & Related Books and Study Guides

#95506 - 09/17/05 07:34 AM Re: Fixture Canopy Fill  
jw electric  Offline
Member
Joined: Sep 2005
Posts: 106
Asheboro, NC
George I would say that if the canopy is not marked with a cu. in. capacity then none.
[Linked Image]


Mike

#95507 - 09/17/05 12:20 PM Re: Fixture Canopy Fill  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
We are required to make all our connections in a "junction box." The fixture canopy, or base, is considered as a "box" when installed.
As such, it is required to have enough space for the usual 6" of 'free conductors." (300.14)

What is not clear is whether there is required to be enough room for a second set of wires to exit, and continue on to the next fixture. It's not even clear if there is required to be room for the switch legs.

A classic example is the "pancake" box....it has room only for wires serving the device; there is no room for these other 'associated' wires.

Personally, I consider it no longer accepted practice to mount a fixture without using a box. Apart from wiring space, the box probides a much better mounting. But I wander....:-)


#95508 - 09/17/05 01:02 PM Re: Fixture Canopy Fill  
Tiger  Offline
Member
Joined: May 2005
Posts: 706
Crystal Lake, IL USA
Article 410.10 is as clear as mud to the issue of your post IMO. It seems to say that, but doesn't really say anything about circuit conductors. The only issue I read in it is...

"shall provide adequate space"

...I don'r read this as limiting at all to other conductors that may occupy the space of the canopy. I'd look for the word ONLY for the meaning you're implying.

Dave


#95509 - 09/17/05 01:06 PM Re: Fixture Canopy Fill  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,080
Estero,Fl,usa
I guess this boils down to the old question, if you terminate 3 #12s in a 6 cu/in pancake can you borrow .75" from the canopy?
Add a .0625" thick ring? (About the thickness of the box material)
... absurd...
If you have 5 wires in there (2H 2N and the grounds) I would have a problem in a pancake, fat canopy or not.


Greg Fretwell