#95287 - 09/06/05 07:21 PM SER Physical protection  
gserve  Offline
Member
Joined: Mar 2003
Posts: 92
Has anyone heard of SER being listed as not needing to be protected from physical protection? Code reference please. Thanks


2017 / 2014 NEC & Related Books and Study Guides

#95288 - 09/06/05 08:24 PM Re: SER Physical protection  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
"Needing protection" is a pretty subjective thing- you're generally stuck with what the AHJ says.

I can think of situations where unprotected, open (insulated) condustors have been in place for decades without harm; I also know of places where schedule 80 steel pipe has prooven inadequate.

The photo forums have countless pics of otherwise code-compliant installations where the components were seriously damaged. Such damage is proof that the original install was not adequate- and, with luck, the repair will provide better protection!

Since you mentioned SER, I can only speculate it is being used to supply power to a service. In that case, the local PoCo rules will also apply. These tend to be much more specific than the NEC, and vary widely from place to place.


#95289 - 09/06/05 09:51 PM Re: SER Physical protection  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Check out 338.10(B)(4)(a) for a guide we need to look at the same protection as needed for NM cable.


George Little

#95290 - 09/07/05 07:08 AM Re: SER Physical protection  
gserve  Offline
Member
Joined: Mar 2003
Posts: 92
I meant to say physical damage. I was told by someone that physical protection is not needed for SER because it is listed as not needing it.


#95291 - 09/07/05 05:57 PM Re: SER Physical protection  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
The someone who told you SE cable doesn't need protection was mistaken. Look at 230.50.


George Little

#95292 - 09/07/05 06:10 PM Re: SER Physical protection  
gserve  Offline
Member
Joined: Mar 2003
Posts: 92
Let me describe the installation. This is a manufactured home. The Service equipment was over 30' away so a disconnect was installed on a 4x4 post next to the home URD was run from the service equipment to the disconnect in PVC. From the back of the disconnect a #2 SER was run under the manufactured home to the 1.5" stub from the panel and they used a 1.5" female PVC adapter and screwed in a 1.5" SER connector into it.They used a PVC 2 hole strap to support it to the frame.


#95293 - 09/07/05 10:44 PM Re: SER Physical protection  
MI Sparky  Offline
Member
Joined: Jul 2005
Posts: 14
Fenton, MI
George, as much as I respect your input, I must disagree. According to your response that would mean every service change that I have ever done that didnt need a riser was illegal, and out of the bottom of every meter can, if it wasnt in conduit, was illegal.

According to 230.50 they shall be protected against physical damage as in (A) Service cables, WHERE SUBJECT TO PHYSICAL DAMAGE, shall be protected by any of the following.....and so on.

At this point, the electrician should know where or where not the cable itself is subject to physical damage.

Let me edit this...on the side of a house, it is not exposed to PHYSICAL DAMAGE, in this case, it is not exposed to damage that I can see.



[This message has been edited by MI Sparky (edited 09-07-2005).]


I thought that was off!!!!

#95294 - 09/07/05 11:17 PM Re: SER Physical protection  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,099
Estero,Fl,usa
This protection thing seems to be regional.
In Md they routinely ran romex on running boards on the walls of garages and utility areas. Service entrance cable was strapped up the wall unprotected.
Here in Florida all of that is going to be in some kind of raceway.


Greg Fretwell

#95295 - 09/08/05 08:21 AM Re: SER Physical protection  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Okay- Let me qualify my answer. The trigger for protection is if the cable is subject to physical damage. This becomes a case by case determination. But to say SE or SER cable don't need physical protection would be not accurate. If it's on the driveway side of a home and the driveway is narrow, maybe a car door opening could cause damage. If it's run through a crawl space it probably wouldn't need physical protection. If it's subject to lawn equipment or storage materials maybe it needs protection. So the answer is definitely/maybe it needs protection [Linked Image]


George Little

#95296 - 09/08/05 11:42 AM Re: SER Physical protection  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,099
Estero,Fl,usa
Sorta like "I can't tell you what it is, but I know it when I see it"


Greg Fretwell

Page 1 of 3 1 2 3

Member Spotlight
Admin
Admin
NY, USA
Posts: 3,447
Joined: October 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 15 (0.003s) Memory: 0.8187 MB (Peak: 0.9906 MB) Zlib enabled. Server Time: 2017-07-23 22:50:48 UTC