#94875 - 08/16/05 07:42 PM sub panel rules  
gserve  Offline
Member
Joined: Mar 2003
Posts: 92
Can someone explain to me the NEC rules on sub panels? What I want to know is the maximum amount of panels if any and maximum size(amps) of each. Example: 200A service and client wants 2 100A subs off of this. Can this be done this way and meet code? Please clarify Thanks


2017 / 2014 NEC & Related Books and Study Guides

#94876 - 08/16/05 07:49 PM Re: sub panel rules  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
There are no NEC rules regarding the number of 'sub panels' or overcurrent devices that can be supplied by a certain size service or feeder.

The only thing that matters is the calculated load.

Wire a house that has 100 outlets, put 10 on a circuit and you end up with 10 breakers.

Now wire the same house but the owner wants each outlet on a home run. You would have 100 outlets with 100 breakers but the calculated load would not have changed.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#94877 - 08/16/05 07:50 PM Re: sub panel rules  
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
Some panels are listed with the maximum current that may be taken from one lug, so you may have to make sure you do not place any breakers opposite the 100-amp breakers.


Larry Fine
Fine Electric Co.
fineelectricco.com

#94878 - 08/16/05 08:53 PM Re: sub panel rules  
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Let's make it three for three. [Linked Image]

Put as many sub fed panels as you want downstream of the main, their cumulative loads are governed by the main itself.

If the main starts tripping on over current, you need to back up.

Roger


#94879 - 08/26/05 12:07 AM Re: sub panel rules  
watersparkfalls  Offline
Member
Joined: Mar 2005
Posts: 220
Washington...Not DC
i thought there was a six switch rule.

h20


#94880 - 08/26/05 05:50 AM Re: sub panel rules  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
H2O, there is a "six switch rule" but that does not have any effect on the number of sub-panels allowed.

With a few exceptions the six switch rule means you must be able to kill the entire building by opening no more than six switches.

As an example if you had a building with a single 200 amp breaker as the service disconnect you would only have to open that one switch in order to kill the entire building regardless of how many sub panels where connected to it.

Think about a very large building, there may be hundreds of sub-panels located throughout the building. But at the service entrance there will be no more than six switches to kill the entire building.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#94881 - 08/26/05 07:14 AM Re: sub panel rules  
Dnkldorf  Offline
Member
Joined: Dec 2004
Posts: 1,064
nowhere usa
Great explanation Bob.......

Dnk....


#94882 - 08/26/05 06:12 PM Re: sub panel rules  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Thank you. [Linked Image]

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#94883 - 08/27/05 12:33 PM Re: sub panel rules  
watersparkfalls  Offline
Member
Joined: Mar 2005
Posts: 220
Washington...Not DC
iwire that makes sense.
now that it was explained in english(vs nec-ism) yuk yuk.

h20



Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.021s Queries: 14 (0.005s) Memory: 0.8008 MB (Peak: 0.9657 MB) Zlib enabled. Server Time: 2017-10-19 07:22:23 UTC