#94021 - 06/30/05 05:56 PM Bollards by a utility transformer  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Quote
Joe:

Is there anywhere in the NEC or the NESC that requires bollards by a utility transformer, or any transformer installation be bonded???

Paul O'Connell


I would check with the local utility company since they may not be covered by the NEC. As far as the NESC, I don't know. I am sure someone will come forward and reply.


Joe Tedesco, NEC Consultant

2017 / 2014 NEC & Related Books and Study Guides

#94022 - 06/30/05 06:24 PM Re: Bollards by a utility transformer  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,826
Brick, NJ USA
Joe:
Our utility (PSE&G) has the bollard requirements spelled out within there specification book. It basically applies to pad mounts that may be subject to physical damage from vehicles.

They also spec bollards to protect CT cabinets, meter equipment etc., that is within their jurisdiction.

These must be NESC rules/requirements.

As to bonding, the utility pad mounts are bonded when they arrive on site; we provide grd rod(s) based on their specs on the primary side.

John


John

#94023 - 06/30/05 08:00 PM Re: Bollards by a utility transformer  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
I repeat Hotline's post: this is a PoCo issue, they are the AHJ...check their standards.

The NEC does require protection from traffic- and that's it. PoCo standards typically tell you how many, how tall, sunk how deep, made how, painted what color, etc. They will also specify WHERE to place the bollards- can't have a bollard blocking line tool access, can we?


#94024 - 07/03/05 11:52 AM Re: Bollards by a utility transformer  
Paul O'Connell  Offline
Member
Joined: Jul 2005
Posts: 56
Allen Park, Mi. USA
I have looked in the NEC, IEEE handbook, NESC handbook,in 40 years I have never seen it done, bollard bonding along with bonding the manhole cover, yet I am being told by a sub contractor for the DOE hired to do NEC inspections that these are both code violations. I would appreciate any input available.



Member Spotlight
Lostazhell
Lostazhell
Bakersfield, CA (Originally Orange Co.)
Posts: 1,429
Joined: February 2004
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.003s) Memory: 0.7609 MB (Peak: 0.8924 MB) Zlib enabled. Server Time: 2017-05-27 13:45:48 UTC