Are concentric or eccentric knockouts evaluated for bonding? #93789
06/18/05 12:06 AM
06/18/05 12:06 AM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Just to be sure, you should read the following information very carefully, when evaluating concentric and eccentric knockouts:
http://www.ul.com/regulators/knockouts.cfm


Joe Tedesco, NEC Consultant
2017 / 2014 NEC & Related Books and Study Guides
Re: Are concentric or eccentric knockouts evaluated for bonding? #93790
06/18/05 03:16 AM
06/18/05 03:16 AM
W
William Runkle  Offline
Member
Joined: Feb 2003
Posts: 27
Dowagiac, Michigan U.S.A.
Intresting have you seen any boxes or cabinets marked? I will be looking for them but I still probably still bond bush so not to upset an inspector who hasn't seen the marking, plus just assurance that it is bonded and be ease of mind.


William Runkle
Re: Are concentric or eccentric knockouts evaluated for bonding? #93791
06/18/05 05:14 PM
06/18/05 05:14 PM
Joe Tedesco  Offline OP
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Yes,

The following table summarizes the box and enclosure categories where such an evaluation is available and how to identify compliant products that can be installed according to the exception to Section 250.97.

Category Code
Product Category
Concentric and eccentric knockouts evaluated for bonding?

BGUZ
Boxes, Junction and Pull
Only when product is marked*

CYIV
Cabinets and Cutout Boxes
Only when product is marked*

QCIT
Metallic Outlet Boxes
All products comply


* Products Listed for these applications are provided with a marking, such as "Concentric (or eccentric) knockouts suitable for bonding conduits for non-service conductors."


Joe Tedesco, NEC Consultant
Re: Are concentric or eccentric knockouts evaluated for bonding? #93792
06/23/05 03:38 PM
06/23/05 03:38 PM
D
DougW  Offline
Member
Joined: Jun 2003
Posts: 1,143
North Chicago, IL
+1 for the additional bonding.

The $8 in parts is worth more than 20 minutes proving your point to an inspector.

Re: Are concentric or eccentric knockouts evaluated for bonding? #93793
06/23/05 04:40 PM
06/23/05 04:40 PM
T
tkb  Offline
Member
Joined: Dec 2004
Posts: 94
Massachusetts
Just knock out the KO all the way and use reducing washers. They are UL listed for grounding. Save the cost of the bond bushings.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,263
Joined: December 2000
Show All Member Profiles 
Top Posters(30 Days)
sparky 23
Admin 20
Potseal 13
Popular Topics(Views)
243,516 Are you busy
180,314 Re: Forum
170,811 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.014s Queries: 14 (0.003s) Memory: 0.9666 MB (Peak: 1.1059 MB) Zlib enabled. Server Time: 2018-01-17 07:07:37 UTC