ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Trumpy 5
Recent Posts
What do you do?
by gfretwell. 09/24/17 12:05 PM
75 kva tranformer
by sparkync. 09/23/17 06:41 PM
Another generator question
by gfretwell. 09/23/17 04:15 PM
Supporting conduit bodies
by ghost307. 09/18/17 12:12 PM
Thermal Imaging Camera upgrade
by Potseal. 09/18/17 11:57 AM
New in the Gallery:
Gallery Test
Popular Topics(Views)
240,956 Are you busy
176,756 Re: Forum
168,602 Need opinion
Who's Online Now
0 registered members (), 73 guests, and 7 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#93774 - 06/14/05 09:07 PM main breaker for subpanel  
Jim M  Offline
Member
Joined: Aug 2001
Posts: 457
Chestertown, MD, USA
I just got a red tag for not having a main in a subpanel in a residential detached garage. Panel is a C-H 4/8 MLO with 2 circuits installed. AHJ is using 225-31 as the reason.

Is anyone elses area requiring this. I guess I was thinking 6 or less breakers did not need a main.


2017 / 2014 NEC & Related Books and Study Guides

#93775 - 06/14/05 09:14 PM Re: main breaker for subpanel  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
In my opinion you are correct.


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#93776 - 06/14/05 09:15 PM Re: main breaker for subpanel  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,118
Estero,Fl,usa
225.33(A) General. The disconnecting means for each supply permitted by 225.30 shall consist of not more than six switches or six circuit breakers mounted in a single enclosure, in a group of separate enclosures, or in or on a switchboard. There shall be no more than six disconnects per supply grouped in any one location.


Greg Fretwell

#93777 - 06/15/05 12:29 AM Re: main breaker for subpanel  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
For a separate building, such as a detached garage, you are required to have a disconnecting means on the building. In this area, I typically have a 'safety switch' mounted on the outside, feeding the panel directly behind it (on the inside). A 'main breaker' in the panel is another way to do it- but is usually more expensive- and our AHJ likes the disconnect on the outside anyway.

There is one exception- no such disconnect is necessary if you're running only one circuit- and "circuit" is vague enough to include a single multi-wire branch circuit (or what we normally think of as two circuits). Assuming that you are using both full-size breaker spaces for a pair of full size breakers, you might be able to argue that you have but a single multi-wire circuit, with the breakers simpling being an additional, not required, disconnecting means.


#93778 - 06/15/05 02:35 PM Re: main breaker for subpanel  
JBD  Offline
Member
Joined: Jul 2001
Posts: 599
WI, USA
IMO (and that of the Handbook) 225 section II effectively says to treat each separate building like it has it's own service entrance. Except when only one circuit (specifically allows multi-wire) is in the separate building.

225.30 only one source can feed the separate building (230.2, 230.40)
225.31 all ungrounded conductors must be disconnected (230.70)
225.32 disconnect where power enters building (230.71(A))
225.33 number of mains (230.71)
225.34 group the mains (230.72)
225.35 accessible to occupants (230.70(A)(1), 230.72(C))
225.36 suitable for service entrance(230.70(C))


#93779 - 06/15/05 03:39 PM Re: main breaker for subpanel  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,118
Estero,Fl,usa
Don't ignore 225.36 exception
Exception: For garages and outbuildings on residential property, a snap switch or a set of 3-way or 4-way snap switches shall be permitted as the disconnecting means.


Greg Fretwell

#93780 - 06/15/05 07:02 PM Re: main breaker for subpanel  
luckyshadow  Offline
Member
Joined: Jan 2005
Posts: 307
Maryland USA
Where I live if the sub panel is in a ATTACHED garage no main needed - in a DETACHED garage a main is required by ahj


#93781 - 06/15/05 08:23 PM Re: main breaker for subpanel  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Thank you, JBD, for taking the time to break down all the code citations I was alluding to!



Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.7936 MB (Peak: 0.9547 MB) Zlib enabled. Server Time: 2017-09-26 16:22:32 UTC