#93221 - 05/09/05 08:02 AM Manhole Cover  
shortcircuit  Offline
Member
Joined: Jun 2004
Posts: 608
massachusetts
If a non-metalic handhole has a metalic cover, is it required to be bonded according to 2005 NEC?

shortcircuit


2017 / 2014 NEC & Related Books and Study Guides

#93222 - 05/09/05 08:39 AM Re: Manhole Cover  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 822
Michigan
Been in a lot of them Utility and Privitely owned Have never seen one Bonded to date.


#93223 - 05/09/05 08:44 AM Re: Manhole Cover  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
See 314.29(D) Covers. Handhole enclosure covers shall have an identifying
mark or logo that prominently identifies the function of
the enclosure, such as “electric.” Handhole enclosure covers
shall require the use of tools to open, or they shall weigh over
45 kg (100 lb). Metal covers and other exposed conductive
surfaces shall be bonded in accordance with 250.96(A).


Joe Tedesco, NEC Consultant

#93224 - 05/09/05 09:29 AM Re: Manhole Cover  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 822
Michigan
Please Post a Pic of a GROUNDED or BONDED manhole cover, I gotta see that!I;m not talking little I;m talking a 8x8x 6ft 6 or so.


#93225 - 05/09/05 01:11 PM Re: Manhole Cover  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
See Article 110, Part V. for Manholes and Other Electric Enclosures Intended
for Personnel Entry, All Voltages

We are discussing "handholes"

I could not find anything in the "manholes" reference above that would satisify your question about them. [Linked Image]


Joe Tedesco, NEC Consultant

#93226 - 05/09/05 02:04 PM Re: Manhole Cover  
Yoopersup  Offline
Member
Joined: Mar 2003
Posts: 822
Michigan
Handholes I agree with but even thoses are going to get interesting , But All the ones I;ve seen to date have had noncontuctive covers. And if The conductors in a lot of cases are pulled right thur then what(if covers metal)??


#93227 - 05/09/05 05:20 PM Re: Manhole Cover  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
While it is rarely done, 250.4(A)(3) requires the manhole cover to be bonded to provide an effective fault clearing path. Note that a large number of the manholes are owned by utilities and not subject to the NEC.
Don


Don(resqcapt19)

#93228 - 05/09/05 06:13 PM Re: Manhole Cover  
shortcircuit  Offline
Member
Joined: Jun 2004
Posts: 608
massachusetts
Guys...sorry...I messed up the topic heading with the wording MANHOLE [Linked Image]

The topic heading was supposed to be HANDHOLE Covers.

I'm interested in what is required by 2005 NEC regarding bonding of metalic handhole covers that are used on non-metalic handhole.

Lets say a concrete precast base with a metalic cover used as a juction box in the ground.

thanx

shortcircuit


#93229 - 05/09/05 07:28 PM Re: Manhole Cover  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Again!

See 314.29(D) Covers. Handhole enclosure covers shall have an identifying
mark or logo that prominently identifies the function of
the enclosure, such as “electric.” Handhole enclosure covers
shall require the use of tools to open, or they shall weigh over
45 kg (100 lb). Metal covers and other exposed conductive
surfaces shall be bonded in accordance with 250.96(A).


Joe Tedesco, NEC Consultant

#93230 - 05/09/05 09:10 PM Re: Manhole Cover  
shortcircuit  Offline
Member
Joined: Jun 2004
Posts: 608
massachusetts
Thanx for the input guys...

So, according to Dons post, 250.4(A)(3) seems to require bonding of this metalic handhole cover used for enclosing electrical conductors...

But, according to Joes post, 250.96(A) seems to only require bonding of this metalic handhole cover if it is to serve as a grounding conductor...

Which rule do I follow?

shortcircuit


Page 1 of 2 1 2

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 15 (0.003s) Memory: 0.8161 MB (Peak: 0.9898 MB) Zlib enabled. Server Time: 2017-04-26 09:57:11 UTC