ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 260 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#93054 04/27/05 08:13 AM
Joined: Feb 2003
Posts: 24
D
Member
I have a existing Hotel. Remodeling the bathrooms, all the wire is ungrounded romex. My question is..
Do I need to run a new 20 amp #12 wire to each bath for the gfi recep, or can I just replace the exsiting recep with a gfi recep?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#93055 04/27/05 08:36 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
The only person that can answer that will be the building department inspecting the job.

The NEC is not retroactive, if the circuit is in place when you get there you can continue to use it.

If it is a new circuit then it must meet the current NEC.

That said you may have local rules that require updating if the remodel is extensive.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#93056 04/27/05 12:15 PM
Joined: Mar 2005
Posts: 399
A
Member
For replacing outlets you might want to check 406.3(D)(2). As an inspector I would be more more interested in the GFI protection than putting them on 20 amp circuits.
Alan


Alan--
If it was easy, anyone could do it.
#93057 04/27/05 04:19 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Alan- you should expand your reference to include 406.3(D)(3)(b).


George Little