Grounding conductor #93038
04/26/05 07:31 PM
04/26/05 07:31 PM
G
GEC-1  Offline OP
Member
Joined: Jun 2001
Posts: 32
Covington, Georgia USA
I cannot find the code article that states that the grounded and grounding conductors may be joined only at the disconnecting means. Can someone help?

2017 / 2014 NEC & Related Books and Study Guides
Re: Grounding conductor #93039
04/26/05 09:04 PM
04/26/05 09:04 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
250.142 kinda says that, At least the concept is there.


George Little
Re: Grounding conductor #93040
04/26/05 09:24 PM
04/26/05 09:24 PM
G
GEC-1  Offline OP
Member
Joined: Jun 2001
Posts: 32
Covington, Georgia USA
Thanks George! I have a friens that is a home inspector who wanted the info.

Re: Grounding conductor #93041
04/27/05 06:49 AM
04/27/05 06:49 AM
W
winnie  Offline
Member
Joined: Sep 2003
Posts: 649
boston, ma
How about 250.24(5) 'Load-Side Grounding Connections. A grounding connection shall not be made to any grounded circuit conductor on the load side of the service disconnecting means except as otherwise permitted in this article.' The FPN points out ranges and dryers, SDS and detached structures.

-Jon

Re: Grounding conductor #93042
05/01/05 01:07 PM
05/01/05 01:07 PM
S
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
250.24(1) says the connection shall be made at any accessible point from the load end of the service drop or lateral to the terminal or bus to which the grounded service conductor is connected at the service disconnecting means.

You do not have to make the connection at the disconnect, it could be made at the weatherhead, meter or any other point as long as it is accessible and is before the service disco.

Re: Grounding conductor #93043
05/02/05 11:32 AM
05/02/05 11:32 AM
A
Alan Nadon  Offline
Member
Joined: Mar 2005
Posts: 399
Elkhart, IN. USA
Sorry Steve,
The BOND between the groundED and groundING must be done IN the service disconnect enclosure.
Before anyone gets mis lead 250.24(A)(1)...connection...made at any accessible point...etc. is refering to the connection of the grounding electrode conductor.
250.24(A)(5)prohibits the connection on the load side of the service disconnect.
250.24(B) & (C) list where the bond between the grounded and grounding is to be done.
It must be done IN the service disconnect enclosure.
Alan--


Alan--
If it was easy, anyone could do it.
Re: Grounding conductor #93044
05/02/05 09:36 PM
05/02/05 09:36 PM
S
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
Alan,

250.24(A) says "A premises wiring system supplied by a grounded ac service shall have a grounding electrode conductor connected to the grounded service conductor, at each service, in accordance with 250.24(A)(1) through (A)(5)."

This section deals with the connection between the grounding electrode conductor and the grounded service conductor, not the connection between the grounding electrode conductor and the grounding electrode.

@50.24(A)(1) says "The connection shall be made at any accessible point from the load end of the service drop or service lateral to and including the terminal or bus to which the grounded service conductor is connected at the service disconnecting means."

This means you can connect the grounding electrode conductor the grounded service conductor at any point from where you make the connection to the utility to the service disconnecting means as long as it is accessible.

To put it in practical terms, are you saying it would not be allowed to connect the cold water ground to the neutral in the metersocket where there are multiple meters and multiple service enclosures? I believe the code would definitely allow this.

Re: Grounding conductor #93045
05/02/05 10:08 PM
05/02/05 10:08 PM
S
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
I have read the post again and realize why Alan answered the way he did. The initial question is not clear as to whether it is the grounding electrode conductor or the equipment grounding conductor.

But I think (maybe not hard enough) that you are referring to the equipment grounding conductor Alan, which is not applicable to the sections you quoted.

250.130 talks about equipment grounding conductor connections and all it says in 250.130(A) is that the connection shall be made by bonding the equipment grounding conductor to the grounded service conductor and the grounding electrode conductor.

It doesn't really specify where this must happen.

Re: Grounding conductor #93046
05/02/05 10:19 PM
05/02/05 10:19 PM
S
Steve T  Offline
Member
Joined: Feb 2001
Posts: 306
Oak Park, IL, USA
Also,

250.24(B) refers to the connection between the grounded conductor and the service enclosure(s)

250.24(C) says the grounding electrode conductor must connect the equipment grounding conductors, the service enclosures, and the grounded conductor to the grounding electrode.

Neither of these sections refer to where the grounding and grounded connections must be made.

Re: Grounding conductor #93047
05/03/05 08:44 AM
05/03/05 08:44 AM
L
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
Around here, we're not allowed to run anything into the meter base (I guess because it's POCO sealed) except the service cable. It would be great if we could connect the grounding electrode conductor here, because it's already outside.

Oh, well.


Larry Fine
Fine Electric Co.
fineelectricco.com
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 259
Joined: February 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 16
Potseal 15
Popular Topics(Views)
243,571 Are you busy
180,369 Re: Forum
170,845 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.052s Queries: 15 (0.005s) Memory: 1.0229 MB (Peak: 1.1985 MB) Zlib enabled. Server Time: 2018-01-21 00:50:05 UTC