ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
twh 10
Admin 4
Recent Posts
Windows 10, who's upgraded?
by ElectricianBud. 05/27/17 11:02 AM
How do you find a good employee?
by ElectricianBud. 05/27/17 10:58 AM
Recall notice: Bosch Solar panels
by ElectricianBud. 05/27/17 10:53 AM
Correct rotation, wrong sequence
by Potseal. 05/27/17 12:15 AM
Dryer, Range grounding from "Main" panel
by sparkync. 05/25/17 05:49 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
236,975 Are you busy
171,988 Re: Forum
164,862 Need opinion
Who's Online Now
0 registered members (), 74 guests, and 10 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#93010 - 04/24/05 06:09 PM Extend pool bonding grid wire  
Micmann  Offline
Member
Joined: Apr 2005
Posts: 20
I just found this site the other day and think it’s great to have a place to air some questions and get some insights on code topics.

I have a question regarding the #8 solid bonding conductor for a pool. I have a customer that has an existing pool and the other day moved the pool pump and heater about 30’ away to the back of a pool cabana. He asked me to relocate the electrical to the back of the cabana as well. I’ll be installing a hand hole to make splices and extend the PVC conduits, however my question is how to extend the #8 solid bond wire since it terminated at the pump. As far as I can see the Code says nothing about the bond wire needing to be “unbroken”. The hand book even shows the pump, railings, diving board, etc being tapped from the run around the pool. The only requirement that I can see in the code is to use a listed pressure connector or clamp or exothermic weld. Since I don’t have the exothermic weld tool available can I use a split bolt rated for direct burial and splice a piece of #8. Or how about a UF splice kit – it’s a pressure connector listed for direct burial (or am I misapplying the term pressure connector?) Any thoughts?

Mic.


2017 / 2014 NEC & Related Books and Study Guides

#93011 - 04/24/05 10:06 PM Re: Extend pool bonding grid wire  
gfretwell  Offline


Member
Joined: Jul 2004
Posts: 9,080
Estero,Fl,usa
They use direct burial listed split bolts around here.


Greg Fretwell

#93012 - 04/25/05 07:53 AM Re: Extend pool bonding grid wire  
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Split bolts here in Michigan too.


George Little

#93013 - 04/25/05 06:33 PM Re: Extend pool bonding grid wire  
abcelectric  Offline
Junior Member
Joined: Apr 2005
Posts: 1
Santa Barbara, CA
The bonding conductor is regularly, and legally connected to the pool reinforcing steel with approved clamps causing a 'breaking' or discontinuation of the conductor. Bonding is a means to assure the equipotential of the conductive surfaces in the pool area, and is different from carrying fault current in service equipment. I would use any kind of equal clamping mechanism, such as a split bolt.



Member Spotlight
renosteinke
renosteinke
Blue Collar Country
Posts: 5,316
Joined: January 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.012s Queries: 14 (0.003s) Memory: 0.7602 MB (Peak: 0.8923 MB) Zlib enabled. Server Time: 2017-05-29 11:31:58 UTC