torque #91303
01/09/05 10:00 AM
01/09/05 10:00 AM
K
kd  Offline OP
Member
Joined: Dec 2004
Posts: 52
When I torque lugs using Aluminum wire, I will apply, say 50 ft. lbs., then several days later check the torque. It will be down to, say, 35 lbs, so I re-torque it. Other ECs say you should just torque it and forget it--that the loss in tightness is built-in to the required torque. Of course Copper holds its torque so it is not a problem. What do you guys and gals say about this?

2017 / 2014 NEC & Related Books and Study Guides
Re: torque #91304
01/09/05 10:47 AM
01/09/05 10:47 AM
Tom  Offline
Member
Joined: Jan 2001
Posts: 1,044
Shinnston, WV USA
Torque it once to the specifications for the lug & leave it alone.


Few things are harder to put up with than the annoyance of a good example.
Re: torque #91305
01/09/05 11:37 AM
01/09/05 11:37 AM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
How does an inspector know how much you've torqued a connection? I am a fan of the break away connection.


George Little
Re: torque #91306
01/10/05 12:38 AM
01/10/05 12:38 AM
P
Physis  Offline
Member
Joined: Dec 2004
Posts: 86
Burlingame, Ca. USA
Another reason to not like aluminum as a conductor.


Sam, San Francisco Bay Area
Re: torque #91307
01/10/05 07:13 PM
01/10/05 07:13 PM
J
John Steinke  Offline
Member
Joined: Apr 2001
Posts: 518
Reno,Nv., USA
Not "another" reason- THE reason! Aluminum is notorious for "creep" when over-torqued. Aluminum should not be torqued to the same values as copper for this reason.
Simply put, too much pressure causes the metal to flow, leaving you with a loose connection. Make sure the value you're using is the correct on, and not "something always used."

Re: torque #91308
01/12/05 12:31 AM
01/12/05 12:31 AM
K
kd  Offline OP
Member
Joined: Dec 2004
Posts: 52
Aluminum association torque table shows the sasme values for Cooper and Aluminum.

Re: torque #91309
01/17/05 08:24 PM
01/17/05 08:24 PM
N
Nick  Offline
Member
Joined: Aug 2001
Posts: 599
Riverside, CA

Re: torque #91310
01/18/05 11:21 AM
01/18/05 11:21 AM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
The following is a very important quote from the document that Nick has posted a link to.
Quote
It is often asked whether bolted connections require periodic retightening. The simple answer is NO. Once the connector is installed with the proper torque, repeated tightening could actually damage the connector and/or the conductor and eventually lead to a failure.

Don


Don(resqcapt19)

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Scott35
Scott35
Anaheim, CA. USA
Posts: 2,708
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
sparky 21
Admin 19
Potseal 13
Popular Topics(Views)
243,514 Are you busy
180,311 Re: Forum
170,804 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.017s Queries: 14 (0.006s) Memory: 0.9905 MB (Peak: 1.1526 MB) Zlib enabled. Server Time: 2018-01-16 23:31:18 UTC