Hot Tub Disconnect #91238
01/06/05 06:21 AM
01/06/05 06:21 AM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 608
massachusetts
If a hot tub is installed on a screened porch of a dwelling and fed with a 50 amp GFCI protected circuit, is a disconnect required near the hot tub?

The 50 amp GFCI breaker isn't within sight of the tub.

shortcircuit

2017 / 2014 NEC & Related Books and Study Guides
Re: Hot Tub Disconnect #91239
01/06/05 07:29 AM
01/06/05 07:29 AM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
Yes disco is needed. 680.12

Re: Hot Tub Disconnect #91240
01/06/05 08:41 AM
01/06/05 08:41 AM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 608
massachusetts
Thanx Electricmanscott...wish they would put that requirement in part 4 also to clear up the confusion that I get from the emergency shutoff rule(680.41)

shortcircuit

Re: Hot Tub Disconnect #91241
01/06/05 10:19 PM
01/06/05 10:19 PM
J
Jim M  Offline
Member
Joined: Aug 2001
Posts: 457
Chestertown, MD, USA
The emergency disconnect is not required at single family dwellings.

Re: Hot Tub Disconnect #91242
01/06/05 10:38 PM
01/06/05 10:38 PM
B
BigB  Offline
Member
Joined: Mar 2004
Posts: 721
Tucson, AZ USA
Jim, you're correct that the emergency disco is not required for single family dwellings however the SERVICE disconnect is still required to be within sight just like any other piece of equipment.

Re: Hot Tub Disconnect #91243
01/10/05 09:46 PM
01/10/05 09:46 PM
H
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
What if there is circuit breakers or switches under the skirt that will disconnect the motor. Do they count?

Re: Hot Tub Disconnect #91244
01/10/05 11:16 PM
01/10/05 11:16 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Yes, the disconnect(s) under the skirt of the spa or hot tub qualify as the required disconnect(s). They/it certainly would be within sight of the equipment served. Some have said that an additional disconnect is needed within sight of the spa or hot tub. The '02 code seems to make it a lot clearer to me by saying "within sight of it's equipment" 680.12 and not "within sight from all pools, spas, and hot tub equipment and shall be located 5' from the inside of the pool, spa, or hot tub" as it did in the '99


George Little
Re: Hot Tub Disconnect #91245
01/11/05 05:52 AM
01/11/05 05:52 AM
S
shortcircuit  Offline OP
Member
Joined: Jun 2004
Posts: 608
massachusetts
George, I think that the disconnect required by 680.12 should be seperate from the tub altogether.What if the hot tub is defective and they want to remove it and replace it with a new one?

shortcircuit

Re: Hot Tub Disconnect #91246
01/11/05 07:09 PM
01/11/05 07:09 PM
M
mike d  Offline
Junior Member
Joined: Jan 2005
Posts: 9
new jersey
680.12 says the disconnecting means shall be
accessible & within sight from its equipment

look at the definition of accessible, I do
not think the disconnect under the spa meets
that requirement.

Re: Hot Tub Disconnect #91247
01/11/05 11:19 PM
01/11/05 11:19 PM
G
George Little  Offline
Member
Joined: Jan 2004
Posts: 1,489
Michigan USA
Wait a minute here- Are we trying to say that the disconnect under the skirt of a spa is not "accessible and within sight of it's equipment" 680.12? I would think that if I'm working on the equipment associated with the disconnect, that I would have the spa/hot tub opened up and this would provides accessibility and within sight. The relationship is between the disconnect and the equipment. You want to install an additional disconnect within sight of the spa/hot tub? Go for it. I'd like to bid against you.


George Little
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Vlado
Vlado
Croatia
Posts: 28
Joined: February 2011
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 15
Popular Topics(Views)
243,606 Are you busy
180,420 Re: Forum
170,875 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 15 (0.004s) Memory: 1.0210 MB (Peak: 1.1955 MB) Zlib enabled. Server Time: 2018-01-24 07:35:08 UTC