#91199 - 01/04/05 01:46 PM Sub panel  
Reel-Break  Offline
Member
Joined: Apr 2002
Posts: 178
nc
While visiting another furum I read a disscusion on sub panels.They must have 4 wires back to the main panel.They also stated in the main panel the neutral and grounds must be separated and not bonded together at main panel.If you have only 3 wire service at the main panel the grounds and neutrals would have to tie or the ground fault path wouldn`t trip the breaker. Did I totally miss something.was it a type o.


2017 / 2014 NEC & Related Books and Study Guides

#91200 - 01/04/05 02:01 PM Re: Sub panel  
electricman2  Offline
Member
Joined: Nov 2003
Posts: 269
Thomasville, NC USA
I believe that either it was misstated in the discussion or you misread it but in the service equipment the EGC's and the service equipment enclosure are bonded to the grounded service conductor (i.e. the neutral). This provides the fault clearing path.


John

#91201 - 01/04/05 07:51 PM Re: Sub panel  
Physis  Offline
Member
Joined: Dec 2004
Posts: 86
Burlingame, Ca. USA
Do you mean:

[1] neutral
[2] (red) leg
[3] (black) leg
[4] Grounding conductor

The service does not provide a grounding conductor. That's why the service has only three conductors. The GEC at the service is where the grounding conductor comes from and it can only be connected to the service neutral at one point and that is at the service.


Sam, San Francisco Bay Area

#91202 - 01/04/05 07:53 PM Re: Sub panel  
Physis  Offline
Member
Joined: Dec 2004
Posts: 86
Burlingame, Ca. USA
After reading your post again. Did they leave out the main bonding jumper?


Sam, San Francisco Bay Area


Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.015s Queries: 14 (0.003s) Memory: 0.7590 MB (Peak: 0.8921 MB) Zlib enabled. Server Time: 2017-07-26 22:40:02 UTC