ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
Top Posters(30 Days)
Potseal 11
Recent Posts
1913 American Electrician's Handbook
by annemarie1. 07/27/17 03:10 PM
600 KW 120/208 3 Phase Y protection
by Yooperup. 07/24/17 12:20 PM
Green House wiring
by ghost307. 07/20/17 09:10 AM
Permit Snafus...AHJs and Contractors Jump in
by HotLine1. 07/18/17 08:06 PM
New in the Gallery:
Housebilding DIY wiring
Popular Topics(Views)
239,371 Are you busy
174,826 Re: Forum
167,216 Need opinion
Who's Online Now
0 registered members (), 52 guests, and 4 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#91067 - 12/27/04 07:24 PM Kitchen counter top receptacles  
Electric Ian  Offline
Member
Joined: Feb 2004
Posts: 133
MA, USA
My understanding of 210.52(B)(3) is that the 20 Amp branch circuits that supply the kitchen contertop receptacles are permitted to supply additional receptacle outlets in the same kitchen, pantry or dining room. What about lighting outlets in the same kitchen. Is it permissible to tap a couple of recessed lights serving the kichen countertop from the 20 Amp branch circuit that supplies the countertop receptacles. I think the answer is no but I want to be sure. 210.52 still confuses me every time I reread it.


2017 / 2014 NEC & Related Books and Study Guides

#91068 - 12/27/04 08:31 PM Re: Kitchen counter top receptacles  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,853
Brick, NJ USA
Ian:
To sum it up; NO

John


John

#91069 - 12/27/04 09:20 PM Re: Kitchen counter top receptacles  
Electric Ian  Offline
Member
Joined: Feb 2004
Posts: 133
MA, USA
Right. Didn't think so - Just wanted confirmation.
Thanks.


#91070 - 12/27/04 09:30 PM Re: Kitchen counter top receptacles  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Here's the commentary from 210.52 B 1-3. It runs a little contrary to Hotlines remarks, but I would avoid adding lighting, or for that matter much else to kit circuits. "These circuits may also supply receptacle outlets in the pantry, dining room, and breakfast room, as well as an electric clock receptacle and electric loads associated with gas-fired appliances, but these circuits are to have no other outlets." meaning lighting etc. Although it requires 2 circuits I often will run 3 or more, depending on customer need or commonsense. And definately leave it seperate from lighting or other appliances like GB/DW.
http://www.markhellerelectric.com/21052B.pdf




[This message has been edited by e57 (edited 12-27-2004).]


Mark Heller
"Well - I oughta....." -Jackie Gleason

#91071 - 12/27/04 09:54 PM Re: Kitchen counter top receptacles  
Electric Ian  Offline
Member
Joined: Feb 2004
Posts: 133
MA, USA
Got it. Thanks e57 for taking the time to make it crystal clear [Linked Image]



Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7682 MB (Peak: 0.9088 MB) Zlib enabled. Server Time: 2017-07-28 08:58:56 UTC