Underwater Pool Light Grounding #90887
12/17/04 08:13 AM
12/17/04 08:13 AM
M
mustangelectric  Offline OP
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
Hi,
I was looking at the NEC for grounding of underwater pool lights and it says that I need an EGC no smaller than #12, is this correct?

Is this fronm the lights to the switch or to the panel?

Thanks for any replies.

-regards

Greg


Electricity has no respect for ignorance!
2017 / 2014 NEC & Related Books and Study Guides
Re: Underwater Pool Light Grounding #90888
12/17/04 12:38 PM
12/17/04 12:38 PM
S
shortcircuit  Offline
Member
Joined: Jun 2004
Posts: 608
massachusetts
The #12 insulated grd should be run from the panel to the pool light juction box or listed transformer...and installed in pipe.

A #8 grd wire from the juction box to the forming shell...

OK?

shortcircuit

Re: Underwater Pool Light Grounding #90889
12/19/04 11:17 AM
12/19/04 11:17 AM
Z
ZR600  Offline
Member
Joined: Apr 2002
Posts: 46
Stevens Point, WI, USA
Must be a solid #8 to the shell.

Re: Underwater Pool Light Grounding #90890
12/19/04 11:22 AM
12/19/04 11:22 AM
P
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
Bonding the forming shell and grounding the pool light are two different issues, both items are addressed in Art 680.

Pierre


Pierre Belarge
Re: Underwater Pool Light Grounding #90891
12/19/04 10:43 PM
12/19/04 10:43 PM
M
mustangelectric  Offline OP
Member
Joined: Feb 2004
Posts: 494
Bentonville, AR
Hi,
The feed is #14 the EGC is #14...The code says #12 for the EGC not the ungrounded or grounded condcutor..

The pool guy is doing this work..

just making sure...

-regards

Greg


Electricity has no respect for ignorance!
Re: Underwater Pool Light Grounding #90892
12/20/04 03:38 PM
12/20/04 03:38 PM
G
gfretwell  Offline

Member
Joined: Jul 2004
Posts: 9,166
Estero,Fl,usa
You need an unspliced #12 from the j box back to the panel
680.23(F)(2)Through-wall lighting assemblies, wet-niche, dry-niche, or no-niche luminaires (lighting fixtures) shall be connected to an insulated copper equipment grounding conductor installed with the circuit conductors. The equipment grounding conductor shall be installed without joint or splice except as permitted in (a)<anpther listed light j box> and (b)<grounding terminals in a switch box that controls the light>. The equipment grounding conductor shall be sized in accordance with Table 250.122 but shall not be smaller than 12 AWG.

He can't splice in a receptacle box or any other box that isn't for switching the light!

As for the ground to the forming shell <in addition to the EGC in the cord> it is either a brass conduit or plastic. If plastic 680.23(B)(2)(b)Nonmetallic Conduit. Where a nonmetallic conduit is used, an 8 AWG insulated solid or stranded copper equipment grounding conductor shall be installed in this conduit unless a listed low-voltage lighting system not requiring grounding is used. The equipment grounding conductor shall be terminated in the forming shell, junction box or transformer enclosure, or ground-fault circuit-interrupter enclosure. The termination of the 8 AWG equipment grounding conductor in the forming shell shall be covered with, or encapsulated in, a listed potting compound to protect the connection from the possible deteriorating effect of pool water.

Note that can be stranded, the ONLY place I know of that specifically allows stranded #8, although some people attempt to make the argument #8 stranded is "larger" than #8 solid thus OK.
I point to 680.26(C) which is pretty unambiguous "(C) Common Bonding Grid. The parts specified in 680.26(B) shall be connected to a common bonding grid with a solid copper conductor, insulated, covered, or bare, not smaller than 8 AWG."


Greg Fretwell

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,142
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 20
sparky 18
Potseal 14
Popular Topics(Views)
243,552 Are you busy
180,359 Re: Forum
170,837 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.062s Queries: 14 (0.044s) Memory: 0.9761 MB (Peak: 1.1224 MB) Zlib enabled. Server Time: 2018-01-19 19:26:13 UTC