#9085 04/16/02 08:26 PM
Joined: Jan 2002
Posts: 1,457
E
Member
May have been covered before but... An inspector told me today that a 15 amp duplex receptacle is not allowed on a 20 amp dedicated circuit. From what I read in the book this would be allowed 210.21(b)(1), (3)because this is not a "single receptacle" as defined by the NEC. He didn't push the issue and signed off on the job but for future reference I would like to hear other opinions.

#9086 04/16/02 08:49 PM
Joined: Mar 2001
Posts: 2,056
R
Member
You're right.