2 ungrounded conductors / 1 means of protection #90829
12/12/04 06:39 PM
12/12/04 06:39 PM
R
rkidd  Offline OP
Junior Member
Joined: Dec 2004
Posts: 2
Atlanta, Ga. USA
I recently cited a double tap (two ungrounded conductors terminating on one 20A breaker) in a service panel as a code violation, but when challanged on it, I can not find it in either the 1999 or the 2002 NEC. I fell like an idiot. Can someone help me out here?


Ray
2017 / 2014 NEC & Related Books and Study Guides
Re: 2 ungrounded conductors / 1 means of protection #90830
12/12/04 06:44 PM
12/12/04 06:44 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
110.3(B) or last sentence of 110.14(A)


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: 2 ungrounded conductors / 1 means of protection #90831
12/12/04 08:14 PM
12/12/04 08:14 PM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
rkidd,

Before citing "double taps" be sure that the breaker is not designed for 2 terminations.
The double tap was commonly cited when I was doing real eatate work. However, some designs such as the "pressure plate" type of termination (Square D uses this) allow 2 conductors of the same size to be terminated on the breaker.

Re: 2 ungrounded conductors / 1 means of protection #90832
12/12/04 08:15 PM
12/12/04 08:15 PM
E
Electric Ian  Offline
Member
Joined: Feb 2004
Posts: 133
MA, USA
This is one of those things that a lot of people in the trade assume is always a code violation. Not necessarily. It is completly dependent on whether or not the circuit breaker is listed for one or two wire. Many 15 and 20Amp circuit breakers are in fact listed to accomodate 2 wires. Reference the link below from the web site of Mike Holt (who probably has more credability than me [Linked Image]
http://www.mikeholt.com/technical.php?id=nec/unformatted/Jan_ECM&type=u&title=NEC%20-%20Question/Answers%20(1-4-2K)

Re: 2 ungrounded conductors / 1 means of protection #90833
12/13/04 12:39 AM
12/13/04 12:39 AM
R
rkidd  Offline OP
Junior Member
Joined: Dec 2004
Posts: 2
Atlanta, Ga. USA
Thank you all for the speedy replys. With these three answers plus the ref. to the Mike Holt site, I get it. I was barking up the wrong tree thinking I would find something that would say only one branch circuit can be protected by one over current device. Thanks again. Ray


Ray

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Show All Member Profiles 
Top Posters(30 Days)
Admin 21
Potseal 15
sparky 15
Popular Topics(Views)
243,595 Are you busy
180,393 Re: Forum
170,863 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.016s Queries: 14 (0.005s) Memory: 0.9665 MB (Peak: 1.1052 MB) Zlib enabled. Server Time: 2018-01-22 22:19:10 UTC